[RE-wrenches] Generator for off grid
Dana
dana at solarwork.com
Mon Jan 24 15:41:05 EST 2011
I use Onan more than Kohler but water cooled and low RPM are
the ticket.
Dana Orzel
Great Solar Works, Inc
E - dana at solarwork.com
V - 970.626.5253
F - 970.626.4140
C - 970.209.4076
web - www.solarwork.com
"Responsible Technologies for Responsible People since 1988"
Do not ever believe anything, but seriously trust through
action.
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf
Of Randy Brooks
Sent: Monday, January 24, 2011 1:16 PM
To: Wrenches RE
Subject: [RE-wrenches] Generator for off grid
Fellow Wrenches,
What generator manufacturer are you currently recommending
for off grid use? A Kohler 18RES (LP, 3,600 rpm, air
cooled) a customer installed last year has already failed
after 370 hours of use during 6 months of construction and
winter occupancy. It consumed enough oil to cause the low
oil shutoff to activate, and the generator controller board
is fried. The owner is still negotiating with Kohler, but
Kohler has said they will not support any of their
generators used off grid.
The owner is looking at a Cummins Onan 20 kW GGMA (LP, 1,800
rpm, liquid cooled).
Any suggestions would be appreciated.
Thanks,
Randy Brooks
Brooks Solar, Inc.
Solar Power for People
140 Columbia View
Chelan, WA 98816
509-682-9646
Randy at BrooksSolar.com
www.BrooksSolar.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20110124/c410de5d/attachment.htm>
More information about the RE-Wrenches
mailing list