[RE-wrenches] Inverter oversizing
Bill Brooks
billbrooks7 at yahoo.com
Wed Jan 19 19:33:00 EST 2011
David,
Good question, but difficult to answer. The basic rule in electronics is
that every 10C hotter that we run something continuously, the overall life
is cut in half. Conversely, if we run inverters cooler, they should last
longer. The difficult question is how much to oversize the inverter to get a
10C temperature drop continuously. Not easy to answer. Also, heat is not the
only killer of an inverter. Line surges and lightning surges are probably
bigger inverter killers. And then there is engineering design. More
inverters have died prematurely for design and quality control reasons than
any other failure type.
The final answer is 42.
Bill.
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Dave Palumbo
Sent: Wednesday, January 19, 2011 3:55 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Inverter oversizing
Bill,
In addition to power production losses due to arrays that are oversized for
the inverter (although within manufacturers specs) how concerned should we
be with shorter inverter service life because the inverter is working at its
maximum?
David Palumbo
Independent Power LLC
462 Solar Way Drive
Hyde Park, VT 05655
www.independentpowerllc.com
NABCEP Certified PV Installer
Vermont Solar Partner
23 Years Experience, (802) 888-7194
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Bill Brooks
Sent: Wednesday, January 19, 2011 6:20 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Inverter oversizing
Kent,
The article that David Brearley cited is a very good discussion on this
subject. It clearly shows the under-prediction of losses due to hitting the
inverter peak power capability when using longer-term data. This study was
done by the Fraunhofer Institute in southern Germany. They get a lot more
clouds there so the results might be comparable to some of the more cloudy
regions of the United States. I would expect the results to be worse in much
of the U.S. that gets clouds and higher irradiation than Freiburg. However,
the results will definitely be less for much of California since clouds
don't happen for sections of the year.
It all matters where you are.
Great discussion.
Bill.
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Kent
Osterberg
Sent: Wednesday, January 19, 2011 1:41 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Inverter oversizing
Bill,
The data are 15 minute averages so I'm sure that some edge of cloud events
are washed out in the average. The energy they contributed was in the total
measurement, but wouldn't have been included in my sum of clipped output.
Observing the data, you can see some edge of cloud effects despite the 15
minute averaging. And on many days I suspect there is edge of cloud effect
that wouldn't have hit the clipping limit too. Obviously, missing some
short interval events biases the results a little but probably not by very
much. For the sake of argument assume that there was a 3 minute, spike in
output 100-watts above my threshold setting. In the 15-minute average that
still would have been a 20-watt bump and with 10-watt data resolution, it
probably would have showed up, but say it didn't show up or that it end up
just below the threshold. Say this happened once every week, not likely,
but if it did the missed data would amount to 0.25 kWhr or about 5% as much
as the total observed with the data clipped at 800 watts. So you have to
really stretch the brief edge of cloud argument to integrate enough energy
to throw my graph off by very much.
Kent Osterberg
Blue Mountain Solar, Inc.
Bill Brooks wrote:
Kent,
How often were your data records? To capture edge of cloud effects, you need
one-second data. Not many people gather that fast or that much data on
inverters. I don't think there is that much energy in these spikes, but they
are real and make some difference. 15-minute average data will completely
wash out this data.
This is also a deficiency in modeling software since most models are using
hourly data.
Bill.
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Kent
Osterberg
Sent: Tuesday, January 18, 2011 1:18 PM
To: Wrenches; Marco Mangelsdorf
Subject: [RE-wrenches] Inverter oversizing
Attached is a graph that I produced to document the effect of various ratios
between the PV array size and the inverter size. I extracted output power
data for a 1020-watt system located in NE Oregon that is on the Sunny Portal
<http://www.sunnyportal.com/Templates/PublicPageOverview.aspx?page=85820a73-
a347-48fb-b8d1-92e5f9b78ab3&plant=608681a7-ef60-4edb-84ff-07110db0ab6a&splan
g=en-US> . The data are publicly accessible so feel free to run your own
analysis. Better yet, analyze the data for a system near you.
Using 2009 data, I looked at how much energy would have been lost if the
output was clipped at 800W, 810W, .... 1020W. I used 2009 data because
there was a period in 2010 when the Sunny Webbox didn't have internet
access. At 800 watts, power clipping would have happened on about 25% of
the days. Yet the energy that would have been lost was only 0.38% of the
annual total.
The results shown on this graph aren't universal, results would be a little
different in 2010, it would be different in some other climate, it would
have been different at another elevation, it would be different with a
different array angle, ..., and the module tolerance and inverter efficiency
also effect the results. Modules in this system are Suntech 170-watt +/-3%.
The inverter is Sunnyboy 1800 that should be operating at close to 93%
efficiency.
Kent Osterberg
Blue Mountain Solar. Inc.
_____
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20110119/cbdae0f1/attachment.htm>
More information about the RE-Wrenches
mailing list