[RE-wrenches] Xantrex PP inverter bypass breakers
Mick Abraham
mick at abrahamsolar.com
Fri Jan 14 12:37:43 EST 2011
Hello, Jeremy or Amy~
The T240 auto-transformer did not ever come factory-installed on a Trace
Power Panel. The T240 was always just a part, but some technicians have
field installed those onto the blank space on a "single inverter" Power
Panel. T240 does incorporate some Square-D breakers and I believe there were
some blank spaces which could be used as desired.
The Square-D Mechanical Interlock allows a "toggle" between two (QO or QOU)
adjacent breakers, so that only one breaker can be "on" at a time. (This
accessory requires that the breaker on the right side is double pole. The LH
breaker can be double pole or single pole.) The part number for the
Mechanical Interlock part is QOU2DTILA.
The Mechanical Interlock was used in the gray box(es) at top of the Trace
Power Panel and in that case the Interlock is working with QO style breakers
plugged into a mini-sized QO breaker box. The gray cover on those mini
breaker boxes was always a funky fit over the breakers inside...something
just didn't seem to line up properly.
The same Mechanical Interlock can also work with QOU (Unit mount) breakers
from Square-D and those are the ones which were used inside the T-240
transformer. The QOU's do not plug into a conventional breaker bus but
instead they have mounting tabs so they can be bolted down, and they accept
a wire on both ends of the breaker.
Proper ampacity rating for AC breakers depends on the transfer switch rating
for the inverter in question. For DR series inverters those breakers were
rated for 30 amps. For SW series inverters the AC breakers were rated for 60
amps.
Breaker model numbers for Square-D begin with the series...QO or QOU in this
case...followed by one digit to indicate the number of poles...followed by
two digits to indicate the ampacity rating. Example: a double pole "unit
mount" style breaker with 30 amp rating would be number QOU230
Jolliness,
Mick Abraham, Proprietor
www.abrahamsolar.com
Voice: 970-731-4675
On Fri, Jan 14, 2011 at 10:19 AM, All Solar, Inc. Jeremy & Amy Rodriguez <
allsolar at scswifi.net> wrote:
> Wrenches,
> I am trying to locate part numbers for the square D breakers and interlock
> used for one of the old power panels from Xantrex with a T240 enclosure ( I
> believe), used as the inverter output / bypass. I also seem to remember
> there is a mounting issue with the breakers also as they come thru the front
> of the 'white' panel's lid.
>
> Thanks in Advance for any help
>
> All Solar Inc.
> Jeremy and Amy Rodriguez
> 1463 M St
> Penrose, CO 81240
> www.asolarelectric.com
> Phone 719-372-3808
> Fax 719-372-3804
> Email allsolar at scswifi.net
> Email allsolar at live.com
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20110114/d86ab19e/attachment.htm>
More information about the RE-Wrenches
mailing list