Why not just use a Magnum MS inverter as a 2nd charger? That way in an
emergency there is a 2nd inverter to cover a failure and it will balance the
loads with or without the PSX 240 most of the time.

I expect the transformer and 2 little chargers cost close to the same as the
inverter and not look as good on the wall either.

Want to speed up battery charging add more inverter / chargers. You could
probably add 2- 4024 Magnums as well as the SW to that large a battery bank
and be fine, but you would want to balance that one.. 

 

Later,

Bob Ellison

 

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Dana
Sent: Thursday, December 09, 2010 11:24 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] 24v Battery Charger 80 Amps?

 

You could add a PSX 240 transformer to balance the generator output and then
add the IOTAs. The PSX240 I think has 6KW output.

 

 

Dana Orzel

Great Solar Works, Inc

E - dana at solarwork.com

V - 970.626.5253

F - 970.626.4140

C - 970.209.4076

web - www.solarwork.com

 

"Responsible Technologies for Responsible People since 1988"

Do not ever belive anything, but seriously trust through action.

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Dave Palumbo
Sent: Thursday, December 09, 2010 9:13 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] 24v Battery Charger 80 Amps?

 

Wrenchsters,

 

Any recommendations on a generator fed Battery Charger for a large 24v
battery bank (1,800AH). It's an existing off grid system with one Trace
SW4024 (has a 120A battery charger). They are getting a larger generator
(14kW) to run shop tools and speed up battery charging. I want to balance
off the second leg of this new generators output with a battery charger that
puts out anywhere from 80 to 100 Amps into the 24v battery bank. 

 

I could use two Iota 24 volt 40 Amp chargers for the 80 Amp max total. 

 

Other options?

 

Dave Palumbo

Independent Power LLC 

www.independentpowerllc.com 

NABCEP Certified PV Installer

Vermont Solar Partner

802.888.7194 

 

 

  _____  

No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1170 / Virus Database: 426/3304 - Release Date: 12/08/10

  _____  

No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1170 / Virus Database: 426/3305 - Release Date: 12/09/10

 

  _____  

No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1170 / Virus Database: 426/3305 - Release Date: 12/09/10

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20101210/1a7bb075/attachment-0001.htm>


More information about the RE-Wrenches mailing list