[RE-wrenches] 3.7kW grid tie

Kirpal Khalsa solarworks at gmail.com
Sun Oct 31 16:34:54 EDT 2010


SMA makes a SunnyBoy 4000US CL (CL for current limited)....This is actually
a 3800 watt inverter with a max continuous output rated at 16A allowing you
to use a 20A backfeed breaker in a 100A panel and still meet the 120%
rule......It should be readily available from SMA but maybe not on the
distributors shelf........
We have used them before to satisfy this requirement with no problems....
Cheers.


-- 
Sunny Regards,
Kirpal Khalsa
NABCEP Certified Solar PV Installer
Renewable Energy Systems
www.oregonsolarworks.com
541-218-0201 m
541-592-3958 o


On Sun, Oct 31, 2010 at 12:58 PM, Glenn Burt <glenn.burt at glbcc.com> wrote:

>  We are opting more and more for supply side connections in these
> situations (assuming convincing the customer that an upgrade to a 200A
> service/panel is not an option). We have yet to run into an AHJ that cannot
> be made to see this is a good option and we use Ilsco Kup-L-Taps to pierce
> the main conductors inside the load center, prior to their landing on the
> main breaker.
>
>
>
> -Glenn Burt
>
> Alteris Renewables, Inc.
>
>
>
> *From:* re-wrenches-bounces at lists.re-wrenches.org [mailto:
> re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *Dave Palumbo
> *Sent:* Sunday, October 31, 2010 2:35 PM
> *To:* 'RE-wrenches'
> *Subject:* Re: [RE-wrenches] 3.7kW grid tie
>
>
>
> AC Point of Connection could be to a backfed 20A DP breaker in the existing
> GE TM3210CCU load center (100A MB with 100A busbar) if the SMA SB3800
> inverter was still available. But a SB4000 requires a 25A breaker which
> violates the 120% rule with the existing panel.
>
> Comments on the options below.
>
>
>
> #1) Go with another 240v grid tie inverter in the 3800W range, so we can
> use a 20 Amp breaker. I see PV Powered and Kaco have 3500’s listed. Any 3.7,
> or 3.8kW inverters?
>
>
>
> #2) Is it possible to either, change out the Main Breaker in the above GE
> load center to a lower amperage MB, or add a Plug In Breaker. There is a GE
> “feeder type” breaker # THQL2190 (90 A DP). Could we use this as the main
> breaker for the load center above? It is listed as a 10KAIC breaker.
>
>
>
> #3) Swap out existing 32 space load center and replace with 150AML panel
> with 100A MB kit.
>
>
>
> Thanks,
>
> Dave Palumbo
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20101031/2731a22a/attachment-0001.htm>


More information about the RE-Wrenches mailing list