[RE-wrenches] Code reference needed
Drake
drake.chamberlin at redwoodalliance.org
Tue Oct 26 21:03:33 EDT 2010
"(3) Height of Working Space. The work space shall be clear and
extend from the grade, floor, or platform to the height required by
110.26(E). Within the height requirements of this section, other
equipment that is associated with the electrical installation and is
located above or below the electrical equipment shall be permitted to
extend not more than 150 mm (6 in.) beyond the front of the
electrical equipment."
At 09:53 AM 10/26/2010, you wrote:
>Allan -
>
>I believe you are referring to NEC 110.26(A)(3) Height of Working Space.
>
>They talk about the 6" plane in that section.
>
>August Goers
>
>Luminalt Energy Corporation
>1320 Potrero Avenue
>San Francisco, CA 94110
>m: 415.559.1525
>o: 415.641.4000
><mailto:august at luminalt.com>august at luminalt.com
>
>From:
><mailto:re-wrenches-bounces at lists.re-wrenches.org>re-wrenches-bounces at lists.re-wrenches.org
>[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Allan Sindelar
>Sent: Monday, October 25, 2010 11:12 PM
>To: RE-wrenches
>Subject: [RE-wrenches] Code reference needed
>
>Wrenches, what's the actual Code reference location for the
>requirement that service equipment be within 6" of the same plane? I
>couldn't find where I expected it in Art. 110.
>Thanks, Allan
>--
>Allan Sindelar
><mailto:Allan at positiveenergysolar.com>Allan at positiveenergysolar.com
>NABCEP Certified Photovoltaic Installer
>EE98J Journeyman Electrician
>Positive Energy, Inc.
>3201 Calle Marie
>Santa Fe, New Mexico 87507
>505 424-1112
><http://www.positiveenergysolar.com/>www.positiveenergysolar.com
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20101026/77fe3e9f/attachment-0001.htm>
More information about the RE-Wrenches
mailing list