[RE-wrenches] Grounding
Nick Soleil
nicksoleilsolar at yahoo.com
Tue Sep 14 12:11:59 EDT 2010
Wrenches:
I use WEEB for Enphase, WEEB lugs and jumpers for the rails, and WEEB for
modules, except with SunPower, which uses the GBL-4DBT. If the lug isn't bolted
on, it probably isn't bonded.
The problem here is UL, not WEEB. I do not share Augusts concerns.
I still feel that the module manufacturers should be responsible for
resolving the grounding and wire management issues. However, I am not holding
my breath.
Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell: 707-321-2937
Office: 707-789-9537
Fax: 707-769-9037
________________________________
From: Mark Frye <markf at berkeleysolar.com>
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Sent: Tue, September 14, 2010 7:05:41 AM
Subject: Re: [RE-wrenches] GEC for Enphase inverters
I believe the AC GEC runs from; the point where the ungrounded current carrying
conductor is bonded to the enclosure of the service enterance equipment; to the
connection to the ground electrode system. Conductors that run from the service
enterance equipment, thru the premis to the Enphase are bonding jumpers that
are not required to be continuous.
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com
________________________________
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of William Miller
Sent: Monday, September 13, 2010 9:46 PM
To: RE-wrenches
Subject: [RE-wrenches] GEC for Enphase inverters
Friends:
According to the 2005 NEC 250.64(C), the GEC for an AC system needs to be
continuous without splices unless they are irreversible. I am not clear where
this conductor starts and ends. Is it from the ground buss in a sub-panel to
the disconnect switch on the roof, or to each inverter?
Also, non-reversible splices need to be listed for use in grounding systems.
Any suggestions on make and model of splices so listed?
Any advise from those more experienced is much appreciated.
William Miller
Please note new e-mail address and domain:
William Miller
Miller Solar
Voice :805-438-5600
email: william at millersolar.com
http://millersolar.com
License No. C-10-773985
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20100914/e6ae12ea/attachment-0001.htm>
More information about the RE-Wrenches
mailing list