[RE-wrenches] GEC for Enphase inverters

Kirk Herander, VSE kirk at vtsolar.com
Tue Sep 14 09:16:42 EDT 2010


William,

 

Here's a link to listed splices made by Burndy, and compared to exothermic
welding.

 

http://portal.fciconnect.com/res/en/pdffiles/brochures/Quick_Ref_Guide.pdf

 

 

Kirk Herander

Vermont Solar Engineering

802.863.1202

NABCEP(tm) Certified Solar Installer

NYSERDA-eligible Installer

VT Solar Incentive Program Partner

  _____  

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of William
Miller
Sent: Tuesday, September 14, 2010 12:46 AM
To: RE-wrenches
Subject: [RE-wrenches] GEC for Enphase inverters

 

Friends:

According to the 2005 NEC 250.64(C), the GEC for an AC system needs to be
continuous without splices unless they are irreversible.  I am not clear
where this conductor starts and ends.  Is it from the ground buss in a
sub-panel to the disconnect switch on the roof, or to each inverter?

Also, non-reversible splices need to be listed for use in grounding systems.
Any suggestions on make and model of splices so listed?

Any advise from those more experienced is much appreciated.

William Miller




Please note new e-mail address and domain:

William Miller 
Miller Solar
Voice :805-438-5600
email: william at millersolar.com
http://millersolar.com <http://millersolar.com/> 
License No. C-10-773985

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20100914/4684dbaa/attachment-0001.htm>


More information about the RE-Wrenches mailing list