[RE-wrenches] Net AC kW Derate Factor for Xantrex XW inverter andXW opinions
Maverick Brown [Maverick Solar]
maverick at mavericksolar.com
Tue Aug 24 22:40:29 EDT 2010
There is a XW6048 double-stack that has 11,760W PV and gets 8200+ W Output
(in our Texas heat) and creates about 60kwh per day.
That 8/11-ish number is right at 70%. I am sure the early spring will be
better.
I also suggest that 400Ah is the minimum battery bank size required for a
proper sell-re that keeps the battery full enough to prevent sulfation, but
limits overvoltage issues in puffy cloud conditions.
Good luck!
Maverick
Maverick Brown
BSEET, NABCEP Certified Solar PV Installer R
President & CEO
Maverick Solar Enterprises, Inc.
12010 West Highway 290, Suite 230, Austin, TX 78737
Office: 512-919-4493
Fax: 512-607-6398
Cell: 512-460-9825
Store: <blocked::http://www.mavericksolar.com/>
http://www.mavericksolar.com
Help: <http://www.mavericksolar.net/> http://www.mavericksolar.net
Corporate: <http://www.mavericksolarenterprises.com/>
http://www.mavericksolarenterprises.com
_____
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Travis
Creswell
Sent: Tuesday, August 24, 2010 4:11 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] Net AC kW Derate Factor for Xantrex XW inverter andXW
opinions
Greetings Esteemed Wrenches,
What would you recommend I use for a total de-rate factor for a grid tied
Xantrex XW system with 4.14 kW of Yingli 230 watt modules? Yingli's are
rated +/- 3% which probably means at least -5% to be safe. Would a total of
.7 be about right? Battery bank will likely be one string of L-16's or
similar.
I'm helping a customer calculate annual production for his rebate. At this
point it's just an estimate as Arkansas wisely bases their rebate on actual
production and requires a dedicated meter for the system. I'm using the
Wiley Asset tool to adjust for shading and azimuth. The Asset software uses
.77 as a default but that's for a battery-less system.
Probably before I head too far down this road what does anyone have to say
about using the XW6048 for a grid tied application? I've used a few XW's
off grid and have been pleased but never grid tied one.
Best,
Travis Creswell
Ozark Energy Services