[RE-wrenches] useful info on wire color coding

R Ray Walters ray at solarray.com
Mon Aug 23 17:02:48 EDT 2010


Please correct me if I'm wrong, but to summarize this issue: 
1) code requires clockwise phase rotation in Panel boards, and AC disconnects, 
2) even though it's not code required, it is good practice to tape those wires black, red, blue, again left to right or clockwise. (as long as you're in the USA)

R. Walters
ray at solarray.com
Solar Engineer




On Aug 23, 2010, at 10:35 AM, Darryl Thayer wrote:

> Hi all I screwed up again
> the code references are
>  Hi leg color 110.15
>  
>  phase location 
>  panel boards  408.3E (left to right ABC with B phase if there is a hi leg B phase)
>  industrial panel boards 409.102B  (same)
>  MCC motor controllers 430.97B    (same)
> 
> Before the code change the Hi-leg was commonly on the Right in my region.  
> A, B, C is clockwise rotation.  But nothing said it would ever be checked, the utility usually does not say, and after it is connected and energized you test at the last disconnect before the motor. 
> 
>  (on a job in 1992 where I had connected several motors including a 200HP, overnight someone had reversed phases to my Main panel board.  I tested before closing the MCC and found with my phase rotation meter the problem, the 200 HP could not be run or even bumped without damage, always check your rotation) 
> 
> --- On Mon, 8/23/10, Darryl Thayer <daryl_solar at yahoo.com> wrote:
> 
> From: Darryl Thayer <daryl_solar at yahoo.com>
> Subject: Re: [RE-wrenches] useful info on wire color coding
> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
> Date: Monday, August 23, 2010, 11:04 AM
> 
> HI all
> it is referenced several times.  
> First 110.15 "Orange or other marking ect"
>     408.3E Panel boards
>     409.120 Industrial panel boards
>     430.80-84 (MCC) Motor Control Centers
> Part of this is from memory, I do not have my code book handy, and as always my memory is not so good
> 
> --- On Mon, 8/23/10, Mark Frye <markf at berkeleysolar.com> wrote:
> 
> From: Mark Frye <markf at berkeleysolar.com>
> Subject: [RE-wrenches] useful info on wire color coding
> To: "'RE-wrenches'" <re-wrenches at lists.re-wrenches.org>
> Date: Monday, August 23, 2010, 9:06 AM
> 
> From: Mark Frye [mailto:markf at berkeleysolar.com] 
> Sent: Sunday, August 22, 2010 6:58 AM
> To: 'RE-wrenches'
> Subject: RE: [RE-wrenches] useful info on wire color coding
> 
> Too lazy to look myself,  but maybe one of you guys with an electronic version of the Code can search for it: a requirement to mark the "stinger" leg of a 240V delta with a 120v neutral tap with orange tape ?
> 
> Mark Frye 
> Berkeley Solar Electric Systems 
> 303 Redbud Way 
> Nevada City,  CA 95959 
> (530) 401-8024 
> www.berkeleysolar.com 
> 
> -----Inline Attachment Follows-----
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
> 
> 
> -----Inline Attachment Follows-----
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20100823/3eb8ee18/attachment-0001.htm>


More information about the RE-Wrenches mailing list