[RE-wrenches] Voltage discrepancy
Exeltech
exeltech at yahoo.com
Fri Aug 20 16:48:40 EDT 2010
Wire gauge isn't the only consideration. Check all crimps and connections in the DC path. A bad one can cause more drop than the wire.
Dan
--- On Fri, 8/20/10, Jeff Oldham <starpower4u at juno.com> wrote:
From: Jeff Oldham <starpower4u at juno.com>
Subject: Re: [RE-wrenches] Voltage discrepancy
To: re-wrenches at lists.re-wrenches.org
Date: Friday, August 20, 2010, 3:43 PM
boB - it is 4' of #6 CU. and the charge rate averages 45A @ 12V nom. I understand that the Vd diff. from 13.6V @ 15A and 14.2V @45A is .1V but the meters when set nuts on at 14.2V are off by at least .3V @ 13.6V. This is not wire sizing issues nor does that explain the calibration drift over a few days.
>From the Solar, Wind and Hydro powered office of Jeff Oldham/Regenerative SOLutions