[RE-wrenches] Gen set problems

Jeff Wongstrom info at thirstylakesolar.com
Thu Jun 24 09:44:09 EDT 2010


Hello William,

As a follow up to a similar problem:

I recently traced the problem to the generator.  With the OB power  
system disconnected from the Kohler 8.5 RES and a halogen lamp  
connected to the generator, voltage surges at shutdown from one phase  
to neutral ranged from 135 to 168VAC.  With the OB system connected  
the surge was 178VAC at shutdown.  No tweaking in the mate allowed  
the inverter to drop input before the surge. A cool down time  
eliminates the surge with an AGS gen stop. To eliminate the surge  
with a manual shutdown from the mate a contactor controlled by the  
AGS signal was installed to interrupt the generator input.



Thirsty Lake Solar
Jeff Wongstrom
NABCEP Certified Solar Installer
University of Montana College of Technology
Renewable Energy Instructor
406-219-1119
thirstylakesolar
energytechnology

On Jun 14, 2010, at 11:31 PM, William Miller wrote:

> Wrenches:
>
> I have a customer that has a problem with a new generator.  He has  
> two VFX3648 inverters in Outback stacking.  He acquired a new  
> generator, a Kohler 12RES, a reputable make and model.  Below is a  
> description of the problem:
>
> The 12RES seems to be operating OK except for one problem.  At the  
> end of a charging cycle, when the gen automatically shuts down and  
> load goes back to the inverters, all lights, TVs, etc., flash, one  
> TV shuts off, and a GFI trips.  This has happened every time.  It  
> did not happen with the 15RES or the smaller back-up gen (which was  
> disconnected manually).  With the 15RES the same GFI would  
> occasionally trip while the unit was charging and handling house  
> load, but never at the auto shutdown point.  I replaced the GFI,  
> but it still trips.  There are three GFIs in the house, but only  
> one--always the same--trips.
>
>
> I suggested he adjust the AC2/Gen transfer delay to a lower  
> number.  He reduced it to minimum and this did not resolve the  
> problem.  I also had him verify that the AC source is selected as  
> generator, which it is.
>
> Do you have any suggestions?
>
> Thanks in advance,
>
> William Miller
>
>
> Please note new e-mail address and domain:
>
> William Miller
> Miller Solar
> Voice :805-438-5600
> email: william at millersolar.com
> http://millersolar.com
> License No. C-10-773985
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re- 
> wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20100624/8d70fa1d/attachment-0001.htm>


More information about the RE-Wrenches mailing list