Wayne,
That's because the GVFX3524 goes not provide any support for ground
switching. If you install a Ground switching relay and isolate the
input neutral from the output neutral bus's this will get rid of this
problem...
On a side note how did you get a utility (or have you) to approve a GT
inverter on a mobile trailer?
Steve Higgins.
Sr Application Engineering Mgr
Sub-Saharan Africa Business Dev Mgr.
Outback Power Systems.
19009 62nd Ave Ne
Arlington Wa 98223
360-618-4313
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Wayne
Irwin
Sent: Tuesday, June 01, 2010 9:30 AM
To: Wrenches
Subject: [RE-wrenches] Portable Solar Trailer w/ intermittent Ground
Fault
Hello Wrenches,
We have a 2KW portable unit with one Outback GVFX3524. Intermittently,
we have a problem feeding GFI breakers.
Its the strangest thing, sometimes it trips GFI's and other times it
doesn't. Aside from the possibility that some of the GFI's aren't wired
properly we haven't been able to figure it out. We have it plugged into
a GFI at the shop (which is wired properly) and there is no problem.
I thought there was a previous string on this issue but could not find
it in the archives.
What do you recommend for grounding portable units and what
recommendations do you have from personal experience?
Thanks!
Wayne Irwin
Director of Engineering
Pure Energy Solar International Inc.
State Licensed Solar Contractor
License # CVC56695
Wayne at PureEnergySolar.com <mailto:PureEnergySolar at hotmail.com>
http://pureenergysolar.com <http://pureenergysolar.net/>
352 377-6527 Office
352 336-3299 Fax
The content of this message is Pure Energy Solar Confidential. If you
are not the intended recipient and have received this message in error,
any use or distribution is prohibited. Please notify me immediately by
reply e-mail and delete this message from your computer system. Thank
you.
________________________________
Hotmail is redefining busy with tools for the New Busy. Get more from
your inbox. See how.
<http://www.windowslive.com/campaign/thenewbusy?ocid=PID28326::T:WLMTAGL
:ON:WL:en-US:WM_HMP:042010_2>
MESSAGE CONFIDENTIALITY NOTICE:
This message (including attachments) is covered by the Electronic Communication Privacy Act, 18 U.S.C. sections 2510-2521, is confidential, and may also be protected by attorney-client or other privilege. If you believe that it has been sent to you in error, please do not read it. If you are not the intended recipient,you are hereby notified that any retention, dissemination, distribution, or copying of this communication is strictly prohibited. Please reply to the sender that you have received the message in error, then delete it. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20100601/8aa5732b/attachment-0001.htm>
More information about the RE-Wrenches
mailing list