Allan,
Square D makes 2-, 3-, and 4-pole models from 30 amps to 1200 amps that are
600Vdc rated. They have by far the most selection of any company at the
moment. The 200-Amp and up versions must pass through two poles of the same
switch. I'm using 3, 2-pole 600A units on 500 kW inverters at the moment. It
all depends on the layout of your combiner boxes. Let me know when you are
ready to do some design work. It ain't residential.
Bill.
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Allan
Sindelar
Sent: Monday, April 12, 2010 4:30 PM
To: August Goers
Cc: RE-wrenches
Subject: Re: [RE-wrenches] 600VDC Safety Switch question
August,
Precisely. And it's a dumb idea, I know. But it's part of a utility-scale
RFP, and it specifically calls out switching the DC input. This is too early
a stage in the process to figure out better approaches; first we have to
qualify for the job.
Surprisingly, Boltswitch makes one, and it's cheaper than SqD. So we may
have found an answer, but I'm still listening for other ideas.
Thank you,
Allan
Allan Sindelar
<mailto:Allan at positiveenergysolar.com> Allan at positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
<http://www.positiveenergysolar.com/> www.positiveenergysolar.com
August Goers wrote:
Allan -
What is the application? Are you trying to switch a large PV array before
the inverter but after the strings have been fused and combined?
-August
August Goers
Luminalt Energy Corporation
O: 415.564.7652
M: 415.559.1525
F: 650.244.9167
<http://www.luminalt.com/> www.luminalt.com
_____
From: <mailto:re-wrenches-bounces at lists.re-wrenches.org>
re-wrenches-bounces at lists.re-wrenches.org [
<mailto:re-wrenches-bounces at lists.re-wrenches.org>
re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Allan Sindelar [
<mailto:allan at positiveenergysolar.com> allan at positiveenergysolar.com]
Sent: Monday, April 12, 2010 12:41 PM
To: RE-wrenches
Subject: [RE-wrenches] 600VDC Safety Switch question
Wrenches,
We need recommendation of a 200A or larger (400A or 600A preferred) two-pole
or three-pole, double-throw, 600VDC rated, manually operated, load-break-
and load-make-rated, service-equipment rated, fusible or nonfusible safety
switch for purposes of switching DC input.
Square D 82345R and H82345 are rated only 250VDC in a fine-print note in
their catalog.
I don't think that what I'm asking for exists, but wiser Wrenches may
prevail. Can anyone suggest another brand and product model that meets these
requirements?
Thank you,
Allan
--
Allan Sindelar
<mailto:Allan at positiveenergysolar.com> Allan at positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
<http://www.positiveenergysolar.com/> www.positiveenergysolar.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20100412/cc483b4d/attachment-0001.htm>
More information about the RE-Wrenches
mailing list