[RE-wrenches] Fwd: Outback Grid Problems
Steve Higgins
shiggins at outbackpower.com
Wed Apr 7 21:26:03 EDT 2010
Sorry Jay... Missed your post.
>From what I understand we changed this between 75 and 76 because of
popping in and out of sell. Ignoring the Temp compensation for Selling
allows the inverter to be a bit more predictable.
Steve Higgins.
Sr Application Engineer.
Sub-Saharan Africa Business Dev Mgr.
Outback Power Systems.
19009 62nd Ave Ne
Arlington Wa 98223
360-618-4313
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of jay
peltz
Sent: Monday, April 05, 2010 3:17 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Fwd: Outback Grid Problems
HI Steve,
Is there a logic to the change between < 75 and 76> regarding loss of
temp comp for Sell RE?
thanks,
jay
peltz power
On Apr 5, 2010, at 2:11 PM, Steve Higgins wrote:
Sell RE and Refloat are not Temp Compensated,
Absorb, Float Voltages and EQ are temp Compensated.
Older Grid tie inverters using firmware revision 75 utilized temperature
compensated voltage with the Sell RE, but new versions such as 76 and
above don't.
"2)What is the difference between refloat and rebulk?"
For the purpose of the GT units, it's really the same. Just when
Refloat, is triggered it's basically going into a Re-bulk mode.
Steve Higgins.
Sr Application Engineer.
Sub-Saharan Africa Business Dev Mgr.
Outback Power Systems.
19009 62nd Ave Ne
Arlington Wa 98223
360-618-4313
MESSAGE CONFIDENTIALITY NOTICE:
This message (including attachments) is covered by the Electronic Communication Privacy Act, 18 U.S.C. sections 2510-2521, is confidential, and may also be protected by attorney-client or other privilege. If you believe that it has been sent to you in error, please do not read it. If you are not the intended recipient,you are hereby notified that any retention, dissemination, distribution, or copying of this communication is strictly prohibited. Please reply to the sender that you have received the message in error, then delete it. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20100407/07fa685f/attachment-0001.htm>
More information about the RE-Wrenches
mailing list