At least for me, the need for and where to put rebar was easier to make
sense of when it was explained to me by a very wise basement contractor that
concrete's strength is compression and weakness is tension.

That's where the steel rebar comes in as it has excellent resistance to
stretching.

For example; engineered prints on basement walls will actually specify the
rebar placed closer to the living space side of the wall.  Imagine the fill
trying to bow the wall like a banana because the footer is holding the
bottom of the wall in place while floor of the house is holding the top in
place.  The fill side of the wall is being compressed and open side is being
stretched.

Hopefully that will help others as much as it did me.

Take care,
Travis Creswell
Ozark Energy Services

-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Kent
Osterberg
Sent: Saturday, March 13, 2010 9:31 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] rebar v/s fiber

The need for rebar or not depends on how the pole is secured and on the 
shape of the footing.  If you are installing a pipe in a deep narrow 
hole per most mount manufacturer's specifications, no rebar should be 
necessary.  Anything else will certainly require rebar and per 
manufacturers' disclaimers should be designed by an engineer.  For 
example, if the installation will have j-bolts in the concrete with the 
post welded to a plate held in place by the j-bolts, a full rebar cage 
will needed.
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




More information about the RE-Wrenches mailing list