I second Mick's appraisal here. I have clients that need 24/7 for computer
but for only a few lighter loads and this has worked out well. They had
frequent outages and very dirty power. They had lost a number of pieces of
equipment to the surges. We used Outback with AGM batteries and a grid tie
feed and they are very pleased.

 

Dana Orzel

 

Great Solar Works, Inc

www.solarwork.com

E - dana at solarwork.com

V - 970.626.5253

F - 970.626.4140

C - 970.209.4076

 

I will be the shift in how the world uses power! - Dana Orzel

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Mick Abraham
Sent: Monday, February 01, 2010 4:30 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Back-up from large grid-tie system.

 

Hello, Holt et al~

If the client only expects 24 hour autonomy, you could build/supply an
"uninterruptible power supply" for the police loads only, with no solar
recharge dedicated to that system. This would involve inverter/chargers,
appropriate safety gear & some monitoring, and a battery bank big enough to
carry those loads for the requested 24 hours...and no PV array. 

When the grid comes back up, that will drive recharge of the battery. If the
client had requested, say, seven days of system autonomy that might point
back to connecting up PV to the system, but for 24 hours of ride-through I
think it's all about the battery...or the generator system with auto
transfer switch per William's suggestion.

Jolliness,

Mick Abraham, Proprietor
www.abrahamsolar.com

Voice: 970-731-4675



On Mon, Feb 1, 2010 at 1:42 PM, <holtek at sbcglobal.net> wrote:

William,

I would agree with generator only if there was the load demand. One thing I
failed to mention is that this will be back-up for lights and communication
for the campus police w/ 24hr autonomy. It looks as though the Sunny Island
route is the most practical at this stage, but I am open for other
suggestions.

 

Holt E. Kelly
Holtek Fireplace & Solar Products
500 Jewell Dr.
Waco TX. 76712
254-751-9111
www.holteksolar.com

----- Original Message ----- 

From: William Miller <mailto:william at millersolar.com>  

To: RE-wrenches <mailto:re-wrenches at lists.re-wrenches.org>  

Cc: RE-wrenches <mailto:re-wrenches at lists.re-wrenches.org>  

Sent: Monday, February 01, 2010 12:18 PM

Subject: Re: [RE-wrenches] Back-up from large grid-tie system.

 

Kelly:

A big a** generator and a transfer switch.

William Miller

PS:  Seriously, I have seen projects like this and rarely is there a natural
subdivision in the power distribution that allows one to back up a portion
of the loads.  Backing up a huge power demand, which I assume this is, is
best done by rotating machinery.

Wm



At 07:52 AM 2/1/2010, holtek at sbcglobal.net wrote:



Project:
43kw system originally designed as grid-tie. 208 3ph, 6 SB7000(208).
Equipment already rec'd.
The curve ball.....client now wants some back-up capabilities that include
solar......there is a 7.92kw sub-array in the system that may be part of the
solution. Any thoughts?



Holt E. Kelly
Holtek Fireplace & Solar Products
500 Jewell Dr.
Waco TX. 76712
254-751-9111
www.holteksolar.com <http://www.holteksolar.com/> 

----- Original Message ----- From: "Peter Parrish"
<peter.parrish at calsolareng.com>
To: <re-wrenches at re-wrenches.org>
Sent: Sunday, January 31, 2010 5:19 PM
Subject: [RE-wrenches] Couple of Qustions about AGM batteries





We have put together a 850 Wdc portable stand-alone PV system. It uses a
Blue Sky 3024DiL charge controller, a pair of SunXtender 250 A-hr AGM
batteries (24 volt configuration), and a Xantrex Prosine 1000 inverter.

We have been using this system for powering "events" and getting some good
marketing from the activities. Everything has worked out well, and the
system is not being used now and probably won't until March or April
sometime.

We have let the system fully charge the batteries through bulk/absorption
and now float. The float conditions are 26.4 V and 2.0 A at a battery
temperature of 21 deg-C.

My first question: is it alright to let the batteries float every day for
the next 6 to 8 weeks, or should I disconnect them from the rest of the
system until we are ready to use the system again?

My second question: since the 3024iL can perform an equalization, is there a
safe equalization procedure for these AGM batteries?

- Peter

Peter T. Parrish, Ph.D., President
California Solar Engineering, Inc.
820 Cynthia Ave., Los Angeles, CA 90065
CA Lic. 854779, NABCEP Cert. 031806-26
peter.parrish at calsolareng.com
Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org/> 


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org <http://www.members.re-wrenches.org/> 



No virus found in this incoming message.
Checked by AVG - www.avg.com <http://www.avg.com/>  
Version: 9.0.733 / Virus Database: 271.1.1/2660 - Release Date: 01/31/10
11:35:00

Please note new e-mail address and domain:

William Miller 
Miller Solar
Voice :805-438-5600
email: william at millersolar.com
http://millersolar.com <http://millersolar.com/> 
License No. C-10-773985

  _____  

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org


_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



 

No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 9.0.733 / Virus Database: 271.1.1/2662 - Release Date: 02/01/10
05:37:00

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20100201/2d68b84b/attachment-0001.htm>


More information about the RE-Wrenches mailing list