[RE-wrenches] FRE Composites instead of rigid conduit
Dana
dana at solarwork.com
Mon Feb 1 17:38:53 EST 2010
Paul -
Is it UL listed?
Is it approved for direct sunlight?
Is it NEC approved?
Fiberglass has not had a good reputation in direct sunlight in my
experience.
I am curious mostly as to its approvals.
Dana Orzel
Great Solar Works, Inc
www.solarwork.com
E - dana at solarwork.com
V - 970.626.5253
F - 970.626.4140
C - 970.209.4076
I will be the shift in how the world uses power! - Dana Orzel
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Paul Lyons
Sent: Monday, February 01, 2010 3:30 PM
To: re-wrenches at lists.re-wrenches.org
Subject: [RE-wrenches] FRE Composites instead of rigid conduit
Esteemed RE-Wrenches:
Have any of you had experience with using fiberglass reinforced epoxy
conduit manufactured by FRE Composites (Quebec, Canada) instead of rigid
conduit on the roof? I am concerned about the manufacturer's claim that the
FRE conduit UV resistance is adequate for rooftop PV installations here in
Massachusetts.
Thanks,
Paul Lyons, P.E.
NABCEP Certified PV Installer
Zapotec Energy Inc.
675 Massachusetts Ave
Cambridge, MA 02139-3309
Tel: 617-547-5900 ext.201
Fax: 617-547-5901
Email: Lyons at ZapotecEnergy.com
No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 9.0.733 / Virus Database: 271.1.1/2662 - Release Date: 02/01/10
05:37:00
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20100201/cf6ba762/attachment-0001.htm>
More information about the RE-Wrenches
mailing list