Hi Chris,
Fairly similar across the range.
Regards,
Jamie
>>> "Chris Worcester" <chris at solarwindworks.com> 1/13/2010 4:14 PM >>>
Hi Jamie,
How do these values correlate to the larger Rolls batteries? We have a
number of the 2-KS-33âs out there along with other various sized large
Rolls battery banks.
Sincerely,
Chris Worcester
Solar Wind Works
NABCEP Certified PV Installer
Phone: 530-582-4503
Fax: 530-582-4603
www.solarwindworks.com
chris at solarwindworks.com
"Proven Energy Solutions"
From:re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of James
Surrette
Sent: Wednesday, January 13, 2010 11:43 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] discharging Rolls batteries
Hi Hugh & Wrenches,
Regarding the charge voltages you sited, you've got the gist.
As battery temperature drops, you need to increase the charge voltage
to properly charge and, conversely, as temperatures rise, voltage needs
to be decreased to reduce the risk of overcharging.
I believe the range we site to accommodate for temperature is (in C);
0-16C: 2.5VPC
17-27C: 2.4VPC
28-40C: 2.36VPC
These are your max bulk / absorb voltage settings.
Regarding a low voltage disconnect, there is a significant difference
between on load and at rest voltages at 50% SOC.
Below is a table of a cell being discharged at a known constant load
(C/20) over time at 25C;
SOC VPC
100% 2.1
75% 2.01
50% 1.93
25% 1.84
0% 1.75
Please note, this is for a cell(s) under constant load and at 25C. If
the load increased, you would see lower voltages more quickly,
Moreover, once the load is removed, resting voltages will increase
dramatically, i.e. 1.75VPC on load will equal ~1.95VPC at rest. If you
were using 2.0VPC (on load) as your cut off, you would only have been
able to discharge ~25% - which does not include capacity reduction due
to temps <25C.......and I know they are lower than that here!
Hope this is of some assistance.
Regards,
Jamie
James Surrette
Surrette Battery Co. Ltd
1 Station Rd.
Springhill, NS, CAN
B0M 1X0
Direct: 902.597.4027
Fax: 902.597.8447
>>> Hugh <hugh at scoraigwind.co.uk> 1/13/2010 2:26 PM >>>
Hi wrenches,
I have been selling and using a few sets of Rolls 4000 series S530
batteries lately.
I have downloaded the Solar Battery manual from www.rollsbattery.com
It's very interesting. At 17 degrees C you need to charge at 14.4
volts. At 16 degrees it's 15 volts. Hmm, Ok I get the idea. I am
certainly learning to compensate my temperatures this winter.
I did a search in the document for the word 'discharge'. I am
cutting off at just below nominal voltage and starting my generator.
I do not get much capacity. A customer has suggested that a lot of
the discharge capacity is to be had at 11.5 volts (he has a 12v
system obviously). Hmm. Sounds a bit harsh. But what voltage
should I be considering to be 50% discharged, and time to start the
genny? And in a hard frost, the same voltage?
No mention of discharge in the solar battery manual. Any ideas anyone?
Please don't tell me to buy an amphour meter (or worse still to sell
them). Those things are way too confusing to calibrate. I can tell
you that I am not getting many amphours out of my batteries in these
low temperatures before the voltage per cell drops below 2.
What do I tell my customers about the end-of-discharge voltage for
sustainable cycling of their Rolls batteries? And is it temp
compensated?
thanks
--
Hugh Piggott
Scoraig Wind Electric
Scotland
http://www.scoraigwind.co.uk
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
This email and its attachments have been scanned by iConnection E-Mail
Firewall for viruses, spam, and malicious content.
The information transmitted in this email is intended only for the
entity or person to which it is addressed and may contain
confidential/privileged material. If you received this in error, please
contact the sender and delete the material from any computer. Any
review, retransmission, dissemination, or other use of this information
by persons or entities other than the intended recipient is strictly
prohibited. %^^%
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20100113/9712918d/attachment-0001.htm>
More information about the RE-Wrenches
mailing list