Yes, we could do that.......however during instances of testing, trouble
shooting, or in the event of a fire it can be helpful to have a wayto quikly
disconnect the inverter from the combiner/fusing *at* the array. In most
standard electrical work having a disconnect located not in line of sight
from location of work leads to lock out/ tag out procedures....I see no
difference here. It prevents one from having an inverter/disconnect from
accidentally being turned on when you are working on the roof out of sight
from a homeowner trying to help, or a co worker not paying attention.
Sunny Regards,
Kirpal
On Mon, Jan 11, 2010 at 5:39 PM, William Miller <william at millersolar.com>
wrote:
> Kirpal:
>
> Can't you disconnect the load at the inverter and then go back to the
array
> to disconnect the feeder?
>
> William
>
> At 04:01 PM 1/11/2010, you wrote:
>
> William.....we love the Outback FWPV12 and 8.......a good improvement
> over the PSPV......we use them high voltage apps, but alas......don't
> open fuse under load.....thats why we need a version which is
> disconnectable......
> Cheers,
>
> --
> Sunny Regards,
> Kirpal Khalsa
> NABCEP Certified Solar PV Installer
> Renewable Energy Systems
> www.oregonsolarworks.com
> 541-218-0201 m
> 541-592-3958 o
>
>
> On Mon, Jan 11, 2010 at 12:16 PM, William Miller
> <william at millersolar.com> wrote:
>> Kirpa:
>>
>> Have you considered using the Outback PSPV combiner with the 600 VDC
>> touch-safe fuse holders and appropriate fuses? I belive this
>> configuration
>> meets the 600 VDC rating.
>>
>> William Miller
>>
>>
>>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20100111/23bc923d/attachment-0001.htm>
More information about the RE-Wrenches
mailing list