Aloha Brian:
   Good luck with Sunvista, if it is in warranty, Sharp will ask you to send it back to them, but they may take 4-8 weeks to return the repaired unit to you!  This can be a big pain, and they often break again.  I just swapped one out for a new GT-3.3 this month, which was easy, but required reconfiguring the strings (from three strings of 7, 7, and 6 to two strings of 10.)
    I don't know what that error code means, but it probably means the inverter is failed.

Nick Soleil
Project Manager
Advanced Alternative Energy Solutions, LLC
PO Box 657
Petaluma, CA 94953
Cell:   707-321-2937
Office: 707-789-9537
Fax:    707-769-9037




________________________________
From: Brian Lupo <brilupo at gmail.com>
To: re-wrenches at lists.re-wrenches.org
Sent: Tue, January 5, 2010 4:25:28 PM
Subject: [RE-wrenches] Sharp Sunvista 3500

Hello all,

This is my first post to this list.  Many thanks for all the information available here, the archives are quite the resource.

Here is my situation....

Sharp Sunvista 3500 power conditioner
error message d-27 

Voltage from the array is proper, roughly 252 vdc per string,
grid 249 ac,
No ground fault,
No bad fuses in external DC disconnect.

We have called tech support and while not elaborating on the exact nature of the problem, they promise a forthcoming call from the warranty dept. tomorrow.

Is d-27 the death knell for this inverter?

Thanks in advance,

Brian 