[RE-wrenches] Battery based hydrogen incidents
jay peltz
jay at asis.com
Wed Dec 15 13:04:33 EST 2010
Hi Dan,
I've see this as well, but I don't put it down to a enclosure problem but a build up inside a individual battery cell,( plugged cap, etc) which IMHO even if the batteries were outside wouldn't help prevent it.
Never the less, why I use eye protection every time I go see batteries.
Jay
peltz power
On Dec 15, 2010, at 9:56 AM, Exeltech wrote:
> 38+ years in RE. Knowledge of one incident (an off-grid friend).
>
> Very sunny day. Very windy. My friend had both PV and a wind generator (still does). He had just stepped out of the room where the batteries were located when (as he described it) he heard something like a loud gunshot. He went back inside to find one of the L16s exploded, top completely blown off, and case broken much of the way down one side.
>
> Had the incident occurred only minutes earlier, injuries could have resulted. He has since relocated his batteries to a dedicated (and vented) battery space.
>
> Dan
>
>
> --- On Wed, 12/15/10, Kent Osterberg <kent at coveoregon.com> wrote:
>
> From: Kent Osterberg <kent at coveoregon.com>
> Subject: Re: [RE-wrenches] Battery based hydrogen incidents
> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
> Date: Wednesday, December 15, 2010, 11:21 AM
>
> Sounds like, in general, that the off-grid industry has been fortunate to not have hydrogen explosions. That's good. No explosions here either. But one shouldn't take that as evidence that it couldn't happen. I don't believe this is a circumstance where it is better to be lucky than good. That's why I recommend doing the calculations.
>
> Kent Osterberg
> Blue Mountain Solar
>
>
>
> Dana wrote:
>>
>> Ken –
>>
>>
>>
>> To meet the flow have run 2 and 3 fans to meet the flow. 2” output from the fan into a 4” header with a matching 2.5” inlet as far away on the lowest portion of the battery box.
>>
>>
>>
>> In 22+ years in off grid installations I have yet to see or even hear of one hydrogen explosion. I get repeatedly asked why we have to go to the efforts we go to for box and venting. I am not able to provide even one incident that I have heard rumor of.
>>
>>
>> Q - How many battery based hydrogen incidents have happened in our collective experience?
>>
>>
>>
>>
>> Dana Orzel
>>
>> Great Solar Works, Inc
>>
>> E - dana at solarwork.com
>>
>> V - 970.626.5253
>>
>> F - 970.626.4140
>>
>> C - 970.209.4076
>>
>> web - www.solarwork.com
>>
>>
>> "Responsible Technologies for Responsible People since 1988"
>>
>> Do not ever belive anything, but seriously trust through action.
>>
>>
>> From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Kent Osterberg
>> Sent: Tuesday, December 14, 2010 12:07 PM
>> To: Wrenches
>> Subject: [RE-wrenches] Battery Venting
>>
>>
>> Fellow Wrenches,
>>
>> The discussion about battery venting reminds me of a useful and inexpensive program, BattMV, for determining ventilation requirements per EN-50272. EN-50272 is a European standard used to determine how much air flow is needed for a room, I don't know of a equivalent standard used in the U.S. It takes a surprising amount of ventilation. For a 400-AH 48-volt L16 bank charged at 57.6 volts and 24 amps, it's about 7 CFM just to keep the %H2 down to 4%. A 12-volt Zephyr vent is good for about 5 CFM! If you think you are venting enough, take some time and study this issue.
>>
>> Kent Osterberg
>> Blue Mountain Solar
>>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20101215/035570cc/attachment.htm>
More information about the RE-Wrenches
mailing list