[RE-wrenches] Battery based hydrogen incidents
jay peltz
jay at asis.com
Wed Dec 15 11:58:25 EST 2010
Hi Dana,
I've been 16 years all offgrid, no reports that I know of.
jay
peltz power
On Dec 15, 2010, at 8:10 AM, Dana wrote:
> Ken –
>
> To meet the flow have run 2 and 3 fans to meet the flow. 2” output from the fan into a 4” header with a matching 2.5” inlet as far away on the lowest portion of the battery box.
>
>
> In 22+ years in off grid installations I have yet to see or even hear of one hydrogen explosion. I get repeatedly asked why we have to go to the efforts we go to for box and venting. I am not able to provide even one incident that I have heard rumor of.
>
> Q - How many battery based hydrogen incidents have happened in our collective experience?
>
>
>
> Dana Orzel
> Great Solar Works, Inc
> E - dana at solarwork.com
> V - 970.626.5253
> F - 970.626.4140
> C - 970.209.4076
> web - www.solarwork.com
>
> "Responsible Technologies for Responsible People since 1988"
> Do not ever belive anything, but seriously trust through action.
>
> From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Kent Osterberg
> Sent: Tuesday, December 14, 2010 12:07 PM
> To: Wrenches
> Subject: [RE-wrenches] Battery Venting
>
> Fellow Wrenches,
>
> The discussion about battery venting reminds me of a useful and inexpensive program, BattMV, for determining ventilation requirements per EN-50272. EN-50272 is a European standard used to determine how much air flow is needed for a room, I don't know of a equivalent standard used in the U.S. It takes a surprising amount of ventilation. For a 400-AH 48-volt L16 bank charged at 57.6 volts and 24 amps, it's about 7 CFM just to keep the %H2 down to 4%. A 12-volt Zephyr vent is good for about 5 CFM! If you think you are venting enough, take some time and study this issue.
>
> Kent Osterberg
> Blue Mountain Solar
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20101215/1a26f638/attachment.htm>
More information about the RE-Wrenches
mailing list