If sealed batteries are inadvertently overcharged, H2 and O may be created at a rate beyond which the two gasses can be recombined within the cells.  In this case, internal seals may open to prevent excessive pressure from accumulating and turning the battery into an explosion hazard.  Venting of the enclosure is needed for the same reason.  Though sealed batteries are less likely to require venting - it's a necessary safety precaution.

Dan


--- On Mon, 12/13/10, jay peltz <jay at asis.com> wrote:

From: jay peltz <jay at asis.com>
Subject: Re: [RE-wrenches] To insulate a battery bank DEPENDS on a lot of factors.
To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
Date: Monday, December 13, 2010, 6:30 PM

Hi Dana,
The manufacturers that I've read, do say they should be in a vented enclosure.But your point is taken,
thanks,
jay

On Dec 13, 2010, at 8:32 AM, Dana wrote:
Sealed batteries do not require a vent , therefore no air passage – less influence of ambient exterior temps to the bank. Perhaps on a small bank this would have an influence.On a large bank in a low usage scenario, IE: second home with no one home, the system may be full by 10AM and the fan runs for most of the day inducing cool air.  Granted most systems have a present [physically] home owner. I have many systems that float for a good part of the winter, awaiting the arrival of either the owner for a week or spring.  Dana OrzelGreat Solar Works, IncE - dana at solarwork.comV - 970.626.5253F - 970.626.4140C - 970.209.4076web - www.solarwork.com  "Responsible Technologies for Responsible People since 1988"Do not ever belive anything, but seriously trust through action.  From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of jay peltz
Sent: Sunday, December 12, 2010 4:49 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] To insulate a battery bank DEPENDS on a lot of factors.  HI Dana,  I'm curious about why you differentiate sealed vs. flooded batteries?   _______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org



-----Inline Attachment Follows-----

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches at lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org




      
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20101214/2c009166/attachment.htm>


More information about the RE-Wrenches mailing list