[RE-wrenches] Head Spinning..(Con) fused.
William Miller
william at millersolar.com
Sun Nov 14 12:54:32 EST 2010
Darryl:
If Aurora can not verify that their inverters will not backfeed the DC
circuitry, then the circuits must be fused. This too is specified in
Berdner's study. We are in agreement.
I think SMA is not the only transformer inverter with a no-backfeed
declaration.
William
At 05:48 AM 11/14/2010, you wrote:
>I never thought I would disagree with William, I have the highest
>admiration for him,
>But the transformerless inverter has no seperation between grid and array,
>no problem if everything is fused.
>Darryl
>--- On Sat, 11/13/10, William Miller <william at millersolar.com> wrote:
>>
>>From: William Miller <william at millersolar.com>
>>Subject: Re: [RE-wrenches] Head Spinning..(Con) fused.
>>To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
>>Date: Saturday, November 13, 2010, 11:26 PM
>>
>>Eric:
>>
>>The best resource I have found on this subject is the white paper that
>>John Berdner wrote. I have a copy on my web site: millersolar.com under
>>Resources.
>>
>>The general rule is no system with two strings combined needs fuses. Run
>>the calcs as presented in the white paper for verification.
>>
>>Just because circuits share a J-box or conduit is not a reason to
>>fuse. Actual connection into an inverter is required before the number
>>of strings is tabulated.
>>
>>William Miller
>>
>>
>>
>>
>>At 08:40 PM 11/13/2010, you wrote:
>>>Wrenches,
>>>
>>>Can anyone shed guidance on the following for me? Should these strings
>>>be fused:
>>>
>>>Total Modules: 44
>>>Total Strings: 4 strings of 11
>>>Total Inverters: 2
>>>
>>>Modules: Silicon Energy 195 Watt @ 8A
>>>Each string feeding an independent MPPT input on an Aurora PVI 4.2kW
>>>Inverter (there are 2 / Aurora)
>>>Inverter is transformerless (READ 690.35 (B))
>>>
>>>Each strings passes through a shared SolaDeck jbox, no combining, and
>>>head directly to their own dedicated GE THN2261RDC DC Disconnect before
>>>entering a dedicated MPPT input on the inverter.
>>>
>>>My big question is 690.9 (A) exception (b) which states I don't need
>>>ocpd as long as "The short circuit currents from all sources do not
>>>exceed the ampacity of the conductors."
>>>
>>>Because all four strings pass through the same jboxs and conduit before
>>>reaching their disconnect and could potentially short together, should I
>>>fuse each string?
>>>
>>>Or am I just up too late reading code....?
>>>
>>>Thanks for being a resource.
>>>
>>>--
>>>Eric Thomas
>>>Solar Epiphany LLC
>>>(206) 919-3014
>>><http://www.solarepiphany.com/>www.solarepiphany.com
>>>
>>>_______________________________________________
>>>List sponsored by Home Power magazine
>>>
>>>List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>>Options & settings:
>>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>>List-Archive:
>>><http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>>List rules & etiquette:
>>><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>>>
>>>Check out participant bios:
>>><http://www.members.re-wrenches.org/>www.members.re-wrenches.org
>>>
>>>
>>>No virus found in this incoming message.
>>>Checked by AVG - <http://www.avg.com/>www.avg.com
>>>Version: 8.5.449 / Virus Database: 271.1.1/3255 - Release Date: 11/13/10
>>>19:34:00
>>Please note new e-mail address and domain:
>>
>>William Miller
>>Miller Solar
>>Voice :805-438-5600
>>email: william at millersolar.com
>><http://millersolar.com/>http://millersolar.com
>>License No. C-10-773985
>>
>>-----Inline Attachment Follows-----
>>
>>_______________________________________________
>>List sponsored by Home Power magazine
>>
>>List Address:
>><http://us.mc519.mail.yahoo.com/mc/compose?to=RE-wrenches@lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>
>>Options & settings:
>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive:
>><http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>>List rules & etiquette:
>>www.re-wrenches.org/etiquette.htm
>>
>>Check out participant bios:
>>www.members.re-wrenches.org
>
>_______________________________________________
>List sponsored by Home Power magazine
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Options & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive:
>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out participant bios:
>www.members.re-wrenches.org
>
>
>No virus found in this incoming message.
>Checked by AVG - www.avg.com
>Version: 8.5.449 / Virus Database: 271.1.1/3255 - Release Date: 11/13/10
>19:34:00
Please note new e-mail address and domain:
William Miller
Miller Solar
Voice :805-438-5600
email: william at millersolar.com
http://millersolar.com
License No. C-10-773985
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20101114/f7380982/attachment.htm>
More information about the RE-Wrenches
mailing list