Hi Jay;

I'd second (3rd, 4th?) everyone else's comments that it probably isn't a good idea.
I'd add that the diode will eat at least a volt, so that's not good for MPPT, or balancing.
The one possible way to do this, might be to use a Vanner battery equalizer, which is designed to split an incoming charge source, and feed 2 batteries, without letting them 
"see" each other. I think they're only good for 24 v, though, so that might not work for your situation. 
The only other way I could see, is using a huge relay ( or paralleled relays) controlled by a C40 (or similar). You would lose both MPPT and PWM, and be back in the solar stone age (90s) though.

TIme to pull out the 2 big cables, and pull 4 smaller ones?
Have fun, I actually like retrofitting old off grid stuff; it presents all sorts of interesting challenges like this.

R. Walters
ray at solarray.com
Solar Engineer




On Oct 20, 2010, at 9:06 AM, jay peltz wrote:

> HI All,
> 
> Say anyone ever paralleled mx/fm-60's?
> 
> I have a unique situation that would be very expensive to pull additional wire however the existing wire is large enough to need 2 fm-60s'
> 
> If I put a diode between them so they don't feed each other any problems that anyone knows of?
> 
> thanks,
> 
> jay
> 
> peltz power
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
> 



More information about the RE-Wrenches mailing list