[RE-wrenches] Supply side connection to a dedicated panel
Dave Palumbo
dave at independentpowerllc.com
Tue Oct 12 00:14:34 EDT 2010
We are installing a 8kW grid tied PV system for a commercial client. There
is an auto start generator on the premises, therefore we will be utilizing a
supply side AC point of connection. Inverter is an SMA SB8000. System owner
plans on adding to system in the next few years. We are designing for a
total of 24kW of PV.
We will install a 200A fused disconnect off the grid feed (line side of the
generator transfer switch). My plan is install a dedicated breaker panel for
the inverter 240VAC output(s). The SB8000 is rated at 29 Amps, so a 40A DP
breaker will do for the point of connection. This panel will eventually have
a total of (3) 40A DP breakers each with 8kW of inverter output.
My question has to do with the interpretation of the 120 percent rule of the
rating of the busbar in the panel. Do I need to use a 225 Amp rated panel
with a downsized 150A main breaker? 225A busbar x 1.2 = 270 Amps -150A MB =
120A total of inverter output allowed. Or, since this panel will only be
used for inverter AC point of connection, and not for loads, is it allowable
to label this panel as a "Dedicated Panel - connect no loads". If that is
the case we could use a 200A panel, or even a 150Amp panel. A local
electrician proposed this "dedicated panel" to avoid the larger load center
panel. I cannot find any mention of "dedicated panel" in the NEC.
I think what I am proposing follows 690.64. Any opinions, or advice would be
appreciated.
Dave Palumbo
Independent Power LLC
www.independentpowerllc.com
NABCEP Certified PV Installer
Vermont Solar Partner
802.888.7194
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20101012/657b651d/attachment.htm>
More information about the RE-Wrenches
mailing list