[RE-wrenches] Tranformless inverter
Hans Frederickson
hans at fredelectric.com
Mon Oct 4 12:16:07 EDT 2010
Ryan,
Yes, there are twice the number of ungrounded conductors, so twice as many
fuses and switches are required. I haven't seen much in the way of combiners
for ungrounded systems... A combiner for an ungrounded system has two fused
ungrounded sections instead of the typical combiner of today which has fuses
on the ungrounded input conductors and just a terminal block for all the
grounded conductors.
-Hans
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Ryan LeBlanc
Sent: Saturday, October 02, 2010 10:52 AM
To: re-wrenches at lists.re-wrenches.org
Subject: Re: [RE-wrenches] Tranformless inverter
Bill,
Specifically, the additional fusing and disconnect requirement you mentions.
Is that each positive and negative PV Source and Output Circuit must have
OCPD and go through switched? Twice the combiner boxes, fuses and switches?
Thanks,
Ryan J. LeBlanc
NABCEPT Certified Solar PV Installer
Cell: 707.591.1950
Direct: 707.536.9839
ryan at NaturalEnergyWorks.com
http://www.NaturalEnergyWorks.com
Ungrounding the array requires additional fusing and disconnects, but the
most significant difference is that the module wiring and all external cable
must be PV Wire/Cable. Therefore only modules with PV Wire/Cable can be used
in these systems. You must confirm from the manufacturer that they have made
the switch. Hopefully all manufacturers will be installing PV Wire/Cable
soon so that this will not be a problem anymore.
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
More information about the RE-Wrenches
mailing list