[RE-wrenches] GEC for Enphase inverters

August Goers august at luminalt.com
Tue Sep 14 20:31:46 EDT 2010


Hi All -

I would just add that having a good c-tap crimping tool on hand is just
about as valuable as it gets in the solar business. I remember holding off
on getting one because of the $200 or $300 price tag but once you have it
you won't believe you lived without it. The possibilities are almost
endless, but we use our crimpers to bond our GECs to the other existing GECs
all the time. Ctaps almost always replace wire nuts when dealing with bare
copper EGCs. The c-taps typically cost less than $5 a pop and always save
that much on labor. Most time when we have a multiple string inverter
installation is makes sense to irreversibly crimp the GECs together and run
one wire back home.

Greenlee, Panduit, etc make good tools and taps. Let me know if you would
like part numbers... -August




On Tue, Sep 14, 2010 at 8:41 AM, Bill Brooks <billbrooks7 at yahoo.com> wrote:

>  Mark and Rebekah,
>
>
>
> The term “continuous” is a requirement for any circuit and implies
> electrical continuity and current-carrying capability. Both the GEC and EGC
> must be continuous or you don’t got one. It is not defined in NEC Article
> 100.
>
>
>
> What most people are referring to when they say that a GEC must be
> continuous is “unbroken” or the NEC talks about “irreversibly spliced.”
> Splicing of a GEC is usually a last resort because there is no other option.
> For instance, multiple bonding jumpers coming off of multiple inverters
> would need to be irreversibly spliced to the main GEC that should proceed
> unbroken from the farthest inverter from the grounding electrode. 250.66 for
> ac and 250.166 for dc are consistent in requiring the minimum GEC to be 8AWG
> copper. Since the GEC for Enphase starts at the inverter on the roof, you
> must have a minimum of 8AWG running among the microinverters and down to the
> grounding electrode system. In the 2008 NEC and 2011 NEC, this conductor can
> serve the purpose of the ac EGC as well and can be terminated on the service
> panel grounding bus.
>
>
>
> Bill.
>
>
>
> *From:* re-wrenches-bounces at lists.re-wrenches.org [mailto:
> re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *Rebekah Hren
> *Sent:* Tuesday, September 14, 2010 7:25 AM
> *To:* RE-wrenches
>
> *Subject:* Re: [RE-wrenches] GEC for Enphase inverters
>
>
>
> The code does require the GEC to be continuous (250.64C), and I believe
> that the AC EGC for the Enphase metal inverter cases is in fact the same as
> the DC GEC since the point of system bonding on the DC side is inside the
> inverter.
>
> See art. 100 definitions:*Grounding Electrode Conductor. A conductor used
> to*
>
> *connect the system grounded conductor...to a point on the grounding
> electrode*
>
> *system.*
>
>
> So this means that for Enphase systems the AC EGC (which is also the DC
> GEC) should be at minimum 8 awg (250.66) and continuous? Seems like it to
> me.
>
>
>
> Rebekah Hren
>
>
>
>
>
> --- On *Tue, 9/14/10, Mark Frye <markf at berkeleysolar.com>* wrote:
>
>
> From: Mark Frye <markf at berkeleysolar.com>
> Subject: Re: [RE-wrenches] GEC for Enphase inverters
> To: "'RE-wrenches'" <re-wrenches at lists.re-wrenches.org>
> Date: Tuesday, September 14, 2010, 10:05 AM
>
> I believe the AC GEC runs from; the point where the ungrounded current
> carrying conductor is bonded to the enclosure of the service enterance
> equipment; to the connection to the ground electrode system. Conductors that
> run from the service enterance equipment, thru the premis to the Enphase are
> bonding jumpers that are not required to be continuous.
>
>
>
> Mark Frye
> Berkeley Solar Electric Systems
> 303 Redbud Way
> Nevada City,  CA 95959
> (530) 401-8024
> www.berkeleysolar.com
>
>
>
>
>  ------------------------------
>
> *From:* re-wrenches-bounces at lists.re-wrenches.org [mailto:
> re-wrenches-bounces at lists.re-wrenches.org] *On Behalf Of *William Miller
> *Sent:* Monday, September 13, 2010 9:46 PM
> *To:* RE-wrenches
> *Subject:* [RE-wrenches] GEC for Enphase inverters
>
> Friends:
>
> According to the 2005 NEC 250.64(C), the GEC for an AC system needs to be
> continuous without splices unless they are irreversible.  I am not clear
> where this conductor starts and ends.  Is it from the ground buss in a
> sub-panel to the disconnect switch on the roof, or to each inverter?
>
> Also, non-reversible splices need to be listed for use in grounding
> systems.  Any suggestions on make and model of splices so listed?
>
> Any advise from those more experienced is much appreciated.
>
> William Miller
>
> *Please note new e-mail address and domain:
>
> *William Miller
> Miller Solar
> Voice :805-438-5600
> email: william at millersolar.com
> http://millersolar.com
> License No. C-10-773985
>
>
> -----Inline Attachment Follows-----
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org<http://mc/compose?to=RE-wrenches@lists.re-wrenches.org>
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>


-- 
August Goers
VP, Engineering

Luminalt Energy Corporation
1320 Potrero Avenue
San Francisco, CA 94110
O: 415.641.4000
M: 415.559.1525
august at luminalt.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20100914/1a2f2ea0/attachment.htm>


More information about the RE-Wrenches mailing list