[RE-wrenches] Advice needed on upsizing a battery & grid interactive inverter stack
Mick Abraham
mick at abrahamsolar.com
Sat Aug 7 19:14:15 EDT 2010
Thanks for the input, Daryl~ For now the prospect is considering sufficient
power for a big energy hog home plus outbuildings. They'll probably get over
that soon once the sticker shock sinks in. You asked, "how big a battery
bank and how big a generator?" Mick replies: the whole hog system would
need...guessing...about 500 kilowatt-hours of storage (~14,000 amp hours at
48 volts), 70kW worth of inverter/charger, plus a lot of PV. A 48 volt
generator seems not best because that would involve over 1,000 amps coming
off the machine. Maybe multiple DC generators would be worth consideration.
I see why you are pointing in that direction, Daryl, because if not for the
generator problem the Outback GT system can go large.
Finding a 48 volt generator line with proper end of charge regulation is
another challenge. Can any List member provide feedback on the Canadian mfr,
Mechron?
Much appreciated,
Mick Abraham, Proprietor
www.abrahamsolar.com
Voice: 970-731-4675
On Sat, Aug 7, 2010 at 11:19 AM, Darryl Thayer <daryl_solar at yahoo.com>wrote:
> I have a functioning Outback system of 12 inverters, the original design
> was for 15 inverters. My system can sell up to 40 kW to the grid and I have
> seen pictures of systems up to 25 inverters. How big a battery bank and how
> big a generator? Realistically you may not want to charge over C/10 Have
> you considered a 48 volt generator?
>
> Daryl
>
> --- On *Fri, 8/6/10, Mick Abraham <mick at abrahamsolar.com>* wrote:
>
>
> From: Mick Abraham <mick at abrahamsolar.com>
> Subject: [RE-wrenches] Advice needed on upsizing a battery & grid
> interactive inverter stack
> To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
> Date: Friday, August 6, 2010, 6:17 PM
>
>
> Yo, Mechanics~
>
> A client is considering a "biggest ever for me" battery based power system.
> They will probably scale down their ambitions once the cost realities settle
> in but for now they've asked me to look for battery based inverter systems
> which can scale bigger than a triple stack of Xantrex XW6048 inverters. Your
> advice would be welcomed.
>
> * The system must be split phase 120/240, not 3 phase.
>
> * Outback seems "out" because the inverter group should handle backup
> battery recharge using grid or generator AC...and we also want to sell
> excess PV power to the grid.
>
> * No cobbled together AC coupled systems would be considered without a
> convincing way to feather the end of charge on the battery when the grid is
> down...float & all. I don't want to go back to the days of clunky, coarse
> battery "end of charge" care.
>
> * Sunny Island/Sunny Boy is in contention but I'm not keen on having to
> stack in pairs to maintain the 120/240 three wire architecture. A single
> Sunny Island failure would take down two of the yellow boxes. What is the
> limit on stack-ability for Sunny Island?
>
> * A battery sales rep suggested Satcon brand but I think that's bogus
> advice. Satcon is pure grid intertie only, right?
>
> ***********************************************
>
> So...there is your challenge de la semaine (challenge of the week). Who
> builds an inverter system with Xantrex XW-like features only bigger...much
> bigger? OR: who could supply the "Mother of Sunny Island/Sunny Boy"
> system? Replies would be welcomed on the List or off.
>
> The Wrench List is the Bomb!
>
> Mick Abraham, Proprietor
> www.abrahamsolar.com
>
> Voice: 970-731-4675
>
> -----Inline Attachment Follows-----
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org<http://mc/compose?to=RE-wrenches@lists.re-wrenches.org>
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20100807/012075e5/attachment.htm>
More information about the RE-Wrenches
mailing list