Sorry all… I was out on a little three day vacation.
I usually program return amps setting to usually 2-3% of the overall battery bank capacity.
Usually and depending on the battery type or manufacure when the current passing from the charger to the battery drops to this Return amp setting technically the batteries are charged.
Because batteries are technically buckets of water with holes in them, they will never stop pulling current, nor will they never be fully charged. What happens is they start to draw a minimum of charge current from the charger. This “Maintenance current” usually is between 2,3,4,5 percent of the overall battery bank capasity.
With the Return amps setting you can get the batteries close to that charged setting.
Steve Higgins.
Sr Application Engineering Mgr
Sub-Saharan Africa Business Dev Mgr.
Outback Power Systems.
19009 62nd Ave Ne
Arlington Wa 98223
360-618-4313
From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Dana
Sent: Thursday, July 22, 2010 8:37 AM
To: 'RE-wrenches'
Subject: [RE-wrenches] RETURN AMP SETTING
Chris Freitas of Outback can you chime in here?
Thanks, Dana Orzel
Great Solar Works, Inc
E - dana at solarwork.com
V - 970.626.5253
F - 970.626.4140
C - 970.209.4076
web - www.solarwork.com
Responsible Technologies for Responsible People since 1988"
From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Darryl Thayer
Sent: Wednesday, July 21, 2010 8:35 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] RETURN AMP SETTING
That is a good question, I have not an answer, but of course it should be based on the amp hour of the battery bank, absorb charging voltage, and of course the charging source in the case of generators. Following Ron's advise start at C/5 for SOC less than 50% then C/10 till about 70% SOC and then C/15 till 80% then C/20 to 90 %. the problem we have no way to set these values, Perhaps Ron could give is a routine? The closet to SOC charging is the Outback and then the Magnum but both miss the goal.
--- On Wed, 7/21/10, Dana <dana at solarwork.com> wrote:
From: Dana <dana at solarwork.com>
Subject: [RE-wrenches] RETURN AMP SETTING
To: "'RE-wrenches'" <re-wrenches at lists.re-wrenches.org>
Date: Wednesday, July 21, 2010, 5:54 PM
As the % of full charge is related to the of degree absorption & gravity [the denser & more charged acid descending, and lighter acid rising] @ what point in the absorption would be prudent to stop charging?
I used to cut off the charge on the Trace SW series at 12 “return amps”, VS. the factory default I think was at 5 amps. This has & continues to work well but I never had anyone really answer this function clearly.
Is there a battery manufacturer or wrench that would care to comment on the:
The minimum “Return” amps to disconnect for a “full” charge?
OR
The time required per 100 AHR after reaching the Absorption point setting for the mix to occur?
I realize that battery construction, battery condition, age and temperature and the current power usage will also play into this factor and it may not be a simple answer.
Dana Orzel
Great Solar Works, Inc
E - dana at solarwork.com
V - 970.626.5253
F - 970.626.4140
C - 970.209.4076
web - www.solarwork.com
Responsible Technologies for Responsible People since 1988"
From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Mark Frye
Sent: Wednesday, July 21, 2010 4:25 PM
To: Allan at positiveenergysolar.com; 'RE-wrenches'
Subject: Re: [RE-wrenches] Propane Generator, Dual Outback Inverters
Allen,
Can I infer that if you are shutting off the gen before charge rates drop in absorption that you are running only briefly in the absorb phase? Or do your charge currents remain high through out an extended absortion phase?
Perhaps you have plenty of PV which you rely upon to bring the batteries up through the absorption phase, once the gen is shut off.
I would be interest to learn more about your approach to this.
Thanks,
Mark Frye
Berkeley Solar Electric Systems
303 Redbud Way
Nevada City, CA 95959
(530) 401-8024
www.berkeleysolar.com <http://www.berkeleysolar.com/>
________________________________
From: re-wrenches-bounces at lists.re-wrenches.org [mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Allan Sindelar
Sent: Wednesday, July 21, 2010 3:17 PM
To: re-wrenches at lists.re-wrenches.org
Subject: Re: [RE-wrenches] Propane Generator, Dual Outback Inverters
The Onan RS20000 shown in the generators article in HP 131 page 98 has performed flawlessly as backup support to an Outback quad-stack of VFX3648s. Differences, however, are that this 20kW gennie charges four inverters, rather than two; the elevation is 6,600 feet for about a 20% output deration; there are no huge loads above charging draw; and the client is aware enough to shut it off before absorption reduces the charge rate - all different conditions than you have described, as the gennie is usually fully loaded and running in balance.
Darryl is right about the amount of words necessary.
Allan Sindelar
Allan at positiveenergysolar.com
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com <http://www.positiveenergysolar.com/>
No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 9.0.851 / Virus Database: 271.1.1/3008 - Release Date: 07/21/10 00:36:00
-----Inline Attachment Follows-----
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 9.0.851 / Virus Database: 271.1.1/3008 - Release Date: 07/21/10 12:36:00
MESSAGE CONFIDENTIALITY NOTICE:
This message (including attachments) is covered by the Electronic Communication Privacy Act, 18 U.S.C. sections 2510-2521, is confidential, and may also be protected by attorney-client or other privilege. If you believe that it has been sent to you in error, please do not read it. If you are not the intended recipient,you are hereby notified that any retention, dissemination, distribution, or copying of this communication is strictly prohibited. Please reply to the sender that you have received the message in error, then delete it. Thank you.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20100726/24c7b7a6/attachment.htm>
More information about the RE-Wrenches
mailing list