[RE-wrenches] Midnite Magnum E-Panel Unofficial Service Bulletin

R Ray Walters ray at solarray.com
Sun Jul 25 01:46:12 EDT 2010


I usually recommend retorqueing all connectors once the panel is mounted. Whether its an E-panel or one we built at the shop, those washboard roads can loosen stuff that would never have had a problem
otherwise. I'm actually surprised we haven't had more problems like this, even with internal wiring on inverters, etc.
Hours of vibration can do bad things to equipment not designed for it.
Having said all that, I too have grown probably too complacent, and forget to check connections, especially if its hard to get to, and the sun is going down.....

R. Walters
ray at solarray.com
Solar Engineer




On Jul 24, 2010, at 1:27 PM, Allan Sindelar wrote:

> Wrenches, 
> In the past month we have encountered some assembly errors on preassembled E-Panels using the Magnum MS4448PAE and MS4024AE inverters. Robin Gudgel has become aware of the problems and has corrected them, but there may be other Wrenches who have installed or plan to install these E-Panels and may be able to correct the errors at installation. Robin has encouraged me to post this here.
> 
> On all three E-Panels the same two problems were found. The first is that the four signal wires (two twisted pairs) connected to the Magnum ME-BMK sending unit for the remote display were loose enough to pull out. In one case this prevented state-of-charge data from being accessible on the display. The solution is simply to tighten the terminals, but as this is a preassembled connection, checking tightness could be overlooked. The second is that the white 14 awg DC - conductor from the preinstalled array GFDI is terminated at the white AC neutral bus. It should be connected to the DC - bus on the shunt. Moving this will require splicing in a few inches of #14 solid white THHN, as the existing conductor is too short, but has a resistor lead soldered to it, discouraging just replacing this wire with a longer piece.
> 
> It's a funny thing - it's easy to overlook these errors because we expect the factory wiring to be correct. I missed these two errors, and so did an experienced installer from our Taos branch who crewed with me on one of the three installations. It took an inexperienced but very skilled apprentice on his first day of his first installation to discover both problems and bring them to my attention. I have worked with Eden, the apprentice, on other projects, so I trusted him to terminate correctly in the E-Panel. Turns out it was his fresh eyes that caught what we had overlooked because we hadn't expected it.
> Allan
> -- 
> Allan Sindelar
> Allan at positiveenergysolar.com
> NABCEP Certified Photovoltaic Installer
> EE98J Journeyman Electrician
> Positive Energy, Inc.
> 3201 Calle Marie
> Santa Fe, New Mexico 87507
> 505 424-1112
> www.positiveenergysolar.com
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20100724/fca8380d/attachment.htm>


More information about the RE-Wrenches mailing list