[RE-wrenches] Additional Battery Charger

bob reellison at gmail.com
Thu Jun 17 21:19:03 EDT 2010


Look into the Magnum inverters as 2nd chargers, very good chargers with
generators.

 

I have done this many times, in the case of failure of the other inverters
for some reason, run wires and be back up and running.

I think the 4448 inverter is 60 amps @ 48 volts with an input of 16 or so
amps AC.

 

Later,

Bob 

 

From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of benn kilburn
Sent: Thursday, June 17, 2010 7:22 PM
To: Wrenches
Subject: [RE-wrenches] Additional Battery Charger

 

G'day Wrenches,

 

 I'm looking for an additional charger(s) to increase the charging capacity
from the back-up 12 kW Onan generator into the 1200 Ah battery.  Right now
the generator's full potential output is limited by the charging capacity of
the two VFX3648's which have a max charge output of 45A each.

 

The idea here is to use the generator to its full charging capacity when it
is running, taking in to consideration that the generator will feed any AC
loads before charging the battery. 

 

Iota and IBE chargers have been suggested.  Any comments on these or other
makes?

 

Do all generator types (diesel, propane, LNG, gasoline) run more efficiently
when fully loaded?  or is this only the case with diesel (so i've heard)?

 

thanks,

benn
DayStar Renewable Energy Inc. 

benn at daystarsolar.ca

780-906-7807 

HAVE A SUNNY DAY 

 

CONFIDENTIALITY NOTICE:    This email, including any attachments, contains
information from DayStar Renewable Energy Inc. and/or its affiliates, which
may be confidential or privileged. The information is intended to be for the
use of the individual or entity named above. If you are not the intended
recipient, be aware that any disclosure, copying, distribution or use of the
contents of this information is prohibited. If you have received this email
in error, please notify the sender immediately by "reply to sender only"
message and destroy all electronic and hard copies of the communication,
including attachments.

 

 

  _____  

Enter for a chance to get your town photo on Bing.ca! Submit
<http://go.microsoft.com/?linkid=9734379>  a Photo Now! 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20100617/6e1a226d/attachment.htm>


More information about the RE-Wrenches mailing list