William,
Check to make sure what Input you have selected... go to
SETUP/FX/INPUT... Verify that you have the Ac Transfer control set to
Gen.
Make sure that you have adjusted the transfer delay cycles in the right
screen... ADV/FX/GEN under Transfer delay cycles... I would set this to
0.
As Mick said.. Check the Lower limit on the AC Voltage... ADV/FX/GEN...
AC2 Gen Lower Limit I would adjust this up to 110-112?
What does he have the cool down timer set to?
I would suggest 5-10 minutes Look under... ADV/MATE/AGS/SETUP... I
would set this to at least 5-10 minutes just to let the genset cool off
before shutting off.
Steve Higgins.
Sr Application Engineering Mgr
Sub-Saharan Africa Business Dev Mgr.
Outback Power Systems.
19009 62nd Ave Ne
Arlington Wa 98223
360-618-4313
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of William
Miller
Sent: Monday, June 14, 2010 10:32 PM
To: RE-wrenches
Subject: [RE-wrenches] Gen set problems
Wrenches:
I have a customer that has a problem with a new generator. He has two
VFX3648 inverters in Outback stacking. He acquired a new generator, a
Kohler 12RES, a reputable make and model. Below is a description of the
problem:
The 12RES seems to be operating OK except for one problem. At the end
of a charging cycle, when the gen automatically shuts down and load goes
back to the inverters, all lights, TVs, etc., flash, one TV shuts off,
and a GFI trips. This has happened every time. It did not happen with
the 15RES or the smaller back-up gen (which was disconnected manually).
With the 15RES the same GFI would occasionally trip while the unit was
charging and handling house load, but never at the auto shutdown point.
I replaced the GFI, but it still trips. There are three GFIs in the
house, but only one--always the same--trips.
I suggested he adjust the AC2/Gen transfer delay to a lower number. He
reduced it to minimum and this did not resolve the problem. I also had
him verify that the AC source is selected as generator, which it is.
Do you have any suggestions?
Thanks in advance,
William Miller
Please note new e-mail address and domain:
William Miller
Miller Solar
Voice :805-438-5600
email: william at millersolar.com
http://millersolar.com
<http://millersolar.com/> License No. C-10-773985
MESSAGE CONFIDENTIALITY NOTICE:
This message (including attachments) is covered by the Electronic Communication Privacy Act, 18 U.S.C. sections 2510-2521, is confidential, and may also be protected by attorney-client or other privilege. If you believe that it has been sent to you in error, please do not read it. If you are not the intended recipient,you are hereby notified that any retention, dissemination, distribution, or copying of this communication is strictly prohibited. Please reply to the sender that you have received the message in error, then delete it. Thank you.