[RE-wrenches] AC wiring loss on micro-inverters
David Brearley
david.brearley at solarprofessional.com
Fri Jun 11 16:04:13 EDT 2010
Maybe Marv can help out here. I¹ve talked with tech support at Enphase and
am under the impression that you can center tap their branch circuits to
reduce voltage drop. This technique was used on a project that we profiled
in SolarPro:
http://solarprofessional.com/article/?file=SP3_2_pg92_Projects_1&search=
David Brearley, Senior Technical Editor
SolarPro magazine
On 6/11/10 2:50 PM, "Nick Soleil" <nicksoleilsolar at yahoo.com> wrote:
> Did you notice that in my calculation I divided the total amperage by 2 to get
> the average ampacity across the string. This seems to be the best way to deal
> with that. Otherwise the loss would have been over 2.8%
>
> Nick Soleil
> Project Manager
> Advanced Alternative Energy Solutions, LLC
> PO Box 657
> Petaluma, CA 94953
> Cell: 707-321-2937
> Office: 707-789-9537
> Fax: 707-769-9037
>
>
>
> From: "markf at berkeleysolar.com" <markf at berkeleysolar.com>
> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Sent: Fri, June 11, 2010 7:02:00 AM
> Subject: Re: [RE-wrenches] AC wiring loss on micro-inverters
>
> Nick,
>
> Good to see other wrenches looking at this issue. However, remember that
> in the interconnect cable between the last and the second to last Enphase,
> the current is small. If you really want to see how the loss is adding up
> you need a more detailed analysis that averages the voltage drop for the
> entire system of interconnect cables.
>
> Mark Frye
> Berkeley solar Electric Systems
>
>> > Hello wrenches and Marv:
>> > How many Enphase inverters do you put on a single parallel string?
>> > The Enphase manual allows for up to 15, but I have found that a single
>> > string of 15 can have very high voltage rise on the AC wiring. Up to
>> > 1.5% loss just on the Enphase cables, and that does not take into
>> > account resistance at the plug connectors or any home-run wiring.
>> > 15 inverters x 190 watts = 2850 watts
>> > 2850 watts / 240 Volts = 11.875 Amps (however at the beginning of the
>> > string it is 0 Amps)
>> > Average Amps on the Enphase cables is 11.875 / 2 = 5.9375 Amps
>> > length of contacts + internal wiring = ~6'
>> > Total Enphase cabling length (6' x 15 inverters) = ~90'
>> > 5.9375 Amps @ 240 V running 90' on #14 AWG CU = 1.4% loss
>> > It is pretty hard to design for 1.5% voltage drop if you have to size for
>> > 0% loss on your wiring! I hope Enphase will increase the size of the wire
>> > in their cables soon. Have you experienced issues with micro-inverters
>> > shutting off due to high AC voltages?
>> >
>> > Nick Soleil
>> > Project Manager
>> > Advanced Alternative Energy Solutions, LLC
>> > PO Box 657
>> > Petaluma, CA 94953
>> > Cell: 707-321-2937
>> > Office: 707-789-9537
>> > Fax: 707-769-9037
>> >
>> >
>> >
>> >
>> > ________________________________
>> > From: i2p <i2p at aol.com>
>> > To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
>> > Sent: Thu, June 10, 2010 4:50:47 PM
>> > Subject: Re: [RE-wrenches] Real world PV production
>> >
>> >
>> >
>> > On Jun 10, 2010, at 7:57:53 AM, "Kelly Keilwitz, Whidbey Sun & Wind"
>> > <kelly at whidbeysunwind.com> wrote:
>> >
>> > PV Watts VASTLY underestimate PV production
>>> >> in our area.
>> > PV Watts underestimates in Central Ca too.
>> >
>> > Don
>> >
>> >
>> > _______________________________________________
>> > List sponsored by Home Power magazine
>> >
>> > List Address: RE-wrenches at lists.re-wrenches.org
>> >
>> > Options & settings:
>> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> >
>> > List-Archive:
>> > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> >
>> > List rules & etiquette:
>> > www.re-wrenches.org/etiquette.htm
>> <http://www.re-wrenches.org/etiquette.htm>
>> >
>> > Check out participant bios:
>> > www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>> >
>> >
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org>
>
>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20100611/a8582bed/attachment.htm>
More information about the RE-Wrenches
mailing list