This is per our AHJ.
Thanks,
Dana Orzel
Great Solar works, Inc.
E - dana at solarwork.com
V - 970.626.5253
F - 970.626.414
C - 970.209.4076
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of benn kilburn
Sent: Wednesday, May 19, 2010 3:21 PM
To: Wrenches
Subject: Re: [RE-wrenches] Enphase System Labeling
Thanks for sharing that Dana,
Are you required by code or the AHJ, for micro-inverter systems, to have an
additional AC d/c aside from the branch circuit breaker? (on the roof or
other location)
For these micro-inverter systems the only labeling required here, by code
(CEC), is;
84-030 (1) which states...
" A warning notice of an interconnected system shall be installed in a
conspicuous place at the supply authority disconnecting means of Rule 84-022
and the supply authority meter location."
84-022 is generally referring to the load center main breaker. And the
utility company puts their own "WARNING: interconnected system" label at the
meter.
So we don't 'have to' provide any additional info, but i think that
providing some is a good idea. As Ray pointed out, too much info can be
discouraging.
For now, I have opted for these labels on the load center as the only
labeling for the system;
Code required -- "WARNING Two Power Source Parallel System" and;
Optional for info -- "Grid-Connected Solar Electric System
Array Rating: 660 WDC
Module Rating (each): 220 WDC"
....the optional one will of course need to be replaced and updated if/when
the owner decides to add to his system.
cheers,
benn
DayStar Renewable Energy Inc.
benn at daystarsolar.ca
780-906-7807
HAVE A SUNNY DAY
_____
From: dana at solarwork.com
To: re-wrenches at lists.re-wrenches.org
Date: Mon, 17 May 2010 14:29:12 -0600
Subject: [RE-wrenches] Enphase System Labeling
This was our last batch
Labeling For Grid-tie Solar Electric System
Great Solar Works, Inc., 970-626-5253
KNOPP SIGNS
Qty - 2, Color red
INTERACTIVE SYSTEM POINT OF INTERCONNECTION
Enphase Micro-Inverters [1] per module [17] Total
PHOTOVOLTAIC SYSTEM SOURCE
PV System Total Watts
3.910 KW
Maximum AC Output Operating Current 13.6
Amps
AC Operating Voltage
240 Volts
For information and service contact:
Great Solar Works, Inc., 970-626-5253
Qty - 1, Color red
PHOTOVOLTAIC SYSTEM SOURCE
PV System Total Watts
3.910 KW
Maximum AC Output Operating Current 13.6
Amps
AC Operating Voltage
240 Volts
For information and service contact:
Great Solar Works, Inc., 970-626-5253
Qty - 1, Color red
PHOTOVOLTAIC AC SYSTEM UTILITY DISCONNECT
WARNING - ELECTRIC SHOCK HAZARD - DONOT TOUCH TERMINALS.
TERMINALS ON BOTH THE LINE AND LOAD SIDES MAY BE ENERGIZED
IN THE OPEN POSITION. IF A GROUND FAULT IS INDICATED THE NORMALLY GROUNDED
CONDUCTORS MAY BE ENERGIZED AND UNGROUNDED
For information and service contact:
Great Solar Works, Inc., 970-626-5253
Qty -1, Color Yellow
PHOTOVOLTAIC SYSTEM CONNECTED
THE AC PV DISCONNECT IS LOCATED
Next to Meter on South Wall
For information and service contact:
Great Solar Works, Inc., 970-626-5253
Thanks, Dana Orzel
Great Solar Works, Inc
E - dana at solarwork.com
V - 970.626.5253
F - 970.626.4140
C - 970.209.4076
web - www.solarwork.com
Responsible Technologies for Responsible People since 1988"
_____
30 days of prizes: Hotmail makes your day easier! Enter now
<http://go.microsoft.com/?linkid=9729704>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20100520/91ef1404/attachment.htm>
More information about the RE-Wrenches
mailing list