[RE-wrenches] current carrying conductor

William Miller william at millersolar.com
Fri May 14 03:12:18 EDT 2010


Marco:

 From the code:

Nonlinear Load. A load where the wave shape of the steady-state current 
does not follow the wave shape of the applied voltage.
FPN: Electronic equipment, electronic/electric-discharge lighting, 
adjustable-speed drive systems, and similar equipment may be nonlinear loads.

Loads with resistor characteristics such as heating loads are 
linear.  Loads with rapid switching are nonlinear, like switching power 
supplies.

Is an inverter non-linear?  I think it is, but that is just a guess.  Also 
poorly defined is the phrase "major portion."

I hope this helps.

William



At 10:23 PM 5/13/2010, you wrote:
>Content-Type: multipart/alternative;
>         boundary="----=_NextPart_000_033C_01CAF2D1.D6D4D700"
>Content-Language: en-us
>
>xmlns:ns0="urn:schemas-microsoft-com:office:smarttags">
>How about some clear definitions-for-dummies of 1) linear loads and 2) 
>non-linear loads?
>
>marco
>
>Marco:
>
>Will non-linear loads be expected?  If so, the neutral is considered to be 
>a current carrying conductor and needs to be counted.  If no non-linear 
>loads, then the neutral is not counted.
>
>Code citation below (2008):
>
>310.15(4) Neutral Conductor.
>(c) On a 4-wire, 3-phase wye circuit where the major
>portion of the load consists of nonlinear loads, harmonic currents
>are present in the neutral conductor; the neutral conductor
>shall therefore be considered a current-carrying conductor.
>
>
>William Miller
>
>PS:  Who's buying dinner, you or your partner?
>
>Wm
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20100514/44088eed/attachment.htm>


More information about the RE-Wrenches mailing list