>>Since the topic of AFI's has come up I wonder if anyone has actually tested one, even an AC one.
>>
>> From what I've read from some tests on the Mike Holt site for AC breakers is that they couldn't get them to work at anything less than standard ISC for the breaker.
>
>I've not tested them, but I have read every patent on AFCI technology I can get my hands on.
>
>They don't sense that the load is arcing, in the sense -- say -- of an electric motor which arcs because of how the brushes work, or any number of other loads which arc. What they detect is arcing current well above the rated ampacity of the circuit breaker. A "series" arc, where the arc is passing through a load, is limited to the load itself -- a 12 amp rated vacuum cleaner makes, maybe, a 12 to 15 amp spike when it arcs. A "parallel" arc, where the arc is passing directly from line to neutral, or line to ground (not all AFCIs include ground-fault detection), will conduct up to the current available from the transformer. However, because it is not a constant load, it doesn't trip the over-current protection of the breaker, the arc just sits there until either it self-extinguishes or it causes a fire.
>
>There have been a lot of discussions on Mike's board about how useless AFCIs are. In the case of RE systems that have significantly less available current (maybe 50 or 100 amps, rather than hundreds to thousands), it's unlikely that a standard AFCI would "see" a high enough current to decide that a "parallel" rather than "series" arc was happening. But if the AHJ wants them, the AHJ gets them ...
>--
>Julie Haugh
>Senior Design Engineer
>greenHouse Computers, LLC // jfh at greenhousepc.com // greenHousePC on Skype