[RE-wrenches] DC wire sizing

R Ray Walters ray at solarray.com
Tue Apr 6 12:16:31 EDT 2010


I agree that we don't want to create the code first, and try and develop the product after. On the other hand, if a DC AFI can be developed that could stop some of the problems I've seen breakers not help, I'm installing them, and pushing for code requirements.
AC GFIs were gimmicky too at first, but now have gone on to save countless lives; usually kids, but a few of us wet booted contractors too.
As far as running things at 100%, I do agree with you, but I also think that 156% over rating in many cases is too much. If the wire and breaker are that oversized, it is less likely to trip when you want it to. 
My most recent damage I saw, the cable a few inches back was in no way damaged, as it only saw array short circuit current, but the connector that arced burned up a whole circuit board.
More oversizing would have only increased the arc potential, and reduced  the chances of a breaker tripping.
Proper sizing (not too big, not too small) is the way.

R. Walters
ray at solarray.com
Solar Engineer




On Apr 6, 2010, at 9:16 AM, robert ellison wrote:

> I have seen info from independent tests that convinces me that AFCI's probably don't work for AC and i hate to think what they would do for DC, if anything. Besides drive the costs up.
> This was a few years ago and maybe they have gotten it together by now.
>  
> Anyone remember the original ground faults form Trace (?) after the code change requiring them in 96? Expensive and prone to catching fire comes to mind, if i remember correctly. Lets not encourage more if that type of experimentation in the industry.
>  
> Just the same i am not a believer of running anything at 100%, it will always have a higher failure rate than something run at a lower capacity, be it a generator, lawn mower or a circuit breaker.
>  
> Bob
>  
>  
>  
>  Mon, Apr 5, 2010 at 5:36 PM, William Miller <william at millersolar.com> wrote:
> Ray:
> 
> It is my analysis that combiner breakers (if present) will protect only wiring upstream of the combiner -- that is, the individual string circuits.  This protection would happen if there is a fault in one individual string (in the wiring or the modules) that allows current from other strings, in excess of the breaker rating, to be supplied through the breaker feeding the faulted string.
> 
> There are two scenarios at play here:
> 
> 1.  Any fault between the combiner and the feeder destination will not trip any circuit breakers.  The breakers are sized such that the current from each individual string is less than the breaker rating (by more than 1.56 times) and they will not open.
> 
> 2.  PV GFDI protection at the destination end of a feeder will not help.  PV GFDI circuits will not remove power from a feeder and they will open the ground-to-grounding conductor bond.
> 
> Analyzing this further:  Fault conditions are made more likely given that PV string circuits are no longer protected by conduit.  Faults are then more likely in individual string circuits (those circuits without conduit protection).  This is most problematic at installations with two or fewer strings, where there is no combiner, i.e. residential installations.  Statistically, residential installations offer greater exposure to electrical fires because: occupancy occurs for more hours per year, fire alarms and sprinklers are often not installed, children are more often present and standards are more lenient for residential wiring systems.
> 
> These two facts are PVs dirty little secrets.  Further innovation is needed...
> 
> William Miller
> 
> 
> 
> At 12:22 PM 4/5/2010, you wrote:
>> I think the 100% rating exception is an interpretation issue. I consider the assembly to be defined as the breaker mounted in its listed enclosure.
>> I agree that the AFIs would add cost, but they might actually offer some protection too. (possibly one AFI unit could offer protection for multiple circuits?)
>> I've never had a PV circuit breaker actually trip, except some nuisance tripping due to faulty breakers.
>> PV breakers seem to only offer protection for very limited situations ie, a short in a PV wire being backfed by enough other PV circuits to trip the breaker.
>> It could happen, but I've never actually seen it. Even completely shattered modules still have enough internal resistance to limit the short circuit current to
>> a value below the breaker trip point.
>> 
>> Ray
>> 
>> On Apr 4, 2010, at 11:47 PM, Kent Osterberg wrote:
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 
> 
> 
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20100406/e2747df8/attachment.htm>


More information about the RE-Wrenches mailing list