[RE-wrenches] Overcurrent Protection on a Subpanel
Dave Click
daveclick at fsec.ucf.edu
Mon Apr 5 09:06:45 EDT 2010
One could interpret that if you have 6 or more inverter breakers getting
combined in a panel, you'd want one main breaker so that you wouldn't
have to turn off all ten individually to disconnect the system.
Something else to ask the AHJ.
Peter Parrish wrote:
> When we use a sub-panel to combine the output of two or more inverters,
> we buy the sub-panel without a main breaker. A wrench who is working
> with us now, recommends buying sub-panels with the main breaker, which
> increases cost by about 50%. Is this a code requirement? Does it depend
> on the distance between the sub- and main panels?
>
> - Peter
>
> Peter T. Parrish, Ph.D., President
> California Solar Engineering, Inc.
> 820 Cynthia Ave., Los Angeles, CA 90065
> CA Lic. 854779, NABCEP Cert. 031806-26
> peter.parrish at calsolareng.com <mailto:peter.parrish at calsolareng.com>
> Ph 323-258-8883, Mobile 323-839-6108, Fax 323-258-8885
>
>
>