The kicker is the large startup, so you may need to use batteries with low internal resistance, such as the Concorde AGM's. You will also have to make sure your cables are good for the max current to avoid any voltage drop which would cause a low voltage shutdown.
Aside from that, just go with around 200-250 AH of battery storage (assuming 12 volts). A pair of golf car size batteries would probably work if they are something like Crown or Trojan.
..................................................................................................
Northern Arizona Wind & Sun - Electricity From The Sun Since 1979
Solar Discussion Forum: http://www.wind-sun.com/ForumVB/
..................................................................................................
----- Original Message -----
From: Mark Dickson
To: 'RE-wrenches'
Sent: Wednesday, March 17, 2010 2:56 PM
Subject: [RE-wrenches] Small Wh and large LRA
Hello Wrenches,
I've been asked to design a battery based PV system for a load that has a high start up surge of about 62A @ 115V. The thing is, once it is running it will only run for ~10 minutes per day at 11A. So the daily loads are very low. How do I size a battery bank large enough to handle the large start-up surge, yet reasonable enough to cover the modest daily load? Is there a rule-of-thumb for this?
Best regards,
Mark Dickson,
NABCEP Certified Solar PV Installer T
Oasis Montana Inc.
------------------------------------------------------------------------------
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20100318/2d1cb822/attachment.htm>
More information about the RE-Wrenches
mailing list