[RE-wrenches] Supply Side Interconnections - Maximum Backfeed
Michael Kelly
mike at solarflair.com
Thu Mar 4 18:02:32 EST 2010
Kirpal,
That was always my interpretation as well. So in the case of a 400A
service, I can backfeed 400A when utilizing a supply side connection.
Others have thoughts on this?
- Mike
--
Michael Kelly
Project Manager / Project Engineer
NABCEP Certified Solar PV Installer ™
SolarFlair Energy, Inc.
11 Mayhew Street
Framingham, MA 01702
Direct Mobile: 617-899-9840
Main Phone: 508-293-4293
Main Fax: 508-293-4003
mike at solarflair.com
On Thu, Mar 4, 2010 at 4:16 PM, Kirpal Khalsa <solarworks at gmail.com> wrote:
> Mike.....i may be wrong....but I think i am right....you are limited by the
> wire size feeding the supply and/or the transformer size which supplies the
> service.....depending on the physical location of the tap you may be limited
> by the enclosure and the enclosure ratings as well
> would love to hear any other ideas...
> Cheers,
> --
> Sunny Regards,
> Kirpal Khalsa
>
> NABCEP Certified Solar PV Installer
> Renewable Energy Systems
> www.oregonsolarworks.com
> 541-218-0201 m
> 541-592-3958 o
>
>
> On Thu, Mar 4, 2010 at 12:50 PM, Michael Kelly <mike at solarflair.com>wrote:
>
>> Hi All,
>>
>> Next to grounding, I find the calculation of the maximum amount of
>> backfeed current allowed in a supply side connection to be the most vague
>> issue in Article 690. Let's assume we have a 400A, 480/277 service in a
>> commercial building, a 400A main service disconnect, and the jurisdiction is
>> under NEC 2008. What is the maximum backfeed current allowed in a supply
>> side connection? The only place the code points you to is 230.82(6), which
>> is no help, or to Article 705, which is no help either. I know that in the
>> draft version of NEC 2011, there is an expansion of 705.12(A) which states "
>> * *Supply Side. An electric power production source shall be permitted to
>> be connected to the supply side of the service disconnecting means as
>> permitted in 230.82(6). The sum of the ratings of all overcurrent devices
>> connected to power production sources shall not exceed the rating of the
>> service." That is a helpful sentence from the Code, but as it is in draft
>> form, what do we do under NEC 2008? What have you used as a maximum
>> backfeed current for supply side connections?
>>
>> Thanks,
>> Mike
>> --
>> Michael Kelly
>> Project Manager / Project Engineer
>> NABCEP Certified Solar PV Installer ™
>>
>> SolarFlair Energy, Inc.
>> 11 Mayhew Street
>> Framingham, MA 01702
>> Direct Mobile: 617-899-9840
>> Main Phone: 508-293-4293
>> Main Fax: 508-293-4003
>> mike at solarflair.com
>>
>> _______________________________________________
>> List sponsored by Home Power magazine
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Options & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
>
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20100304/52d85f00/attachment.htm>
More information about the RE-Wrenches
mailing list