[RE-wrenches] single string of batts: must the interconnects be inverter size cables?

Phil Undercuffler solarphil at gmail.com
Fri Feb 19 14:28:37 EST 2010


The interconnects are part of the circuit.  Typical flexible cables used
with batteries are THW rated (75C column), so in free air 2/0 interconnects
would be good for 265 amps, before any temperature derates.  Therefore,
you'd be safe from a NEC point of view.  However, if the inverter
manufacturer has recommended 4/0 cables, then that recommendation would
apply to all cables in the circuit.  Battery based inverters are asked to
surge many times their rated capacity -- a 24V 4kW inverter surging to 2x
capacity (pretty normal circumstances) is going to draw over 360 amps (8,000
/ 22), even if only for a short period of time.  You don't want your
interconnects to be the weak link in the system, causing shutdowns due to
undervoltage unnecessarily.

I'd use 4/0.

Phil Undercuffler
Conergy





On Fri, Feb 19, 2010 at 12:01 PM, Mick Abraham <mick at abrahamsolar.com>wrote:

> Example: 12 two volt battery cells in one 24 volt string. 4kW
> inverter/charger has 250 amp DC breaker size and 4/0 cables...as the
> inverter folks would want.
>
> So...do the "cell to cell" interconnect cables have to also be 4/0? In the
> example above, 2/0 interconnects would suffice from the standpoint of basic
> safety...and even from the voltage drop standpoint...right?
>
> Inverter company people may be best qualified to answer this, but any
> replies will be appreciated. While I'm at it: do the inverter folks request
> oversize cables because they want more capacitance on the DC input...or
> what?
>
> Jolliness,
>
> Mick Abraham, Proprietor
> www.abrahamsolar.com
>
> Voice: 970-731-4675
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20100219/b2533527/attachment.htm>


More information about the RE-Wrenches mailing list