[RE-wrenches] Load or Line Side was Solar accumulation panel

William Miller william at millersolar.com
Wed Jan 13 22:51:05 EST 2010


Carl:

You are correct.  I had the exact argument with an inspector.  Here is what 
I did to make a convincing argument:  I opened the disconnect and then 
reached in and touched the load side contacts (inverter side) with my 
fingers.  I turned to the inspector and said, "Now it's your turn to touch 
the line side."  Case closed.

William Miller


At 05:17 PM 1/13/2010, you wrote:
>Wrenches,
>
>I just had an AHJ require me to switch the load and line connections
>on the fused AC disconnect which sits between the inverters (AC
>Combiner panel)  and the point of utility connection.  The inverter
>was connected on the LOAD side of the fused disconnect, and while the
>AHJ agreed this was the safest configuration, (when the disco is OFF
>the fuses are safe to remove) he insisted that the PV array should be
>connected to the LINE side of the disconnect since it is supplying
>power rather than acting as a LOAD.  Any similar experience or
>arguments I can make based on the NEC which might help change the
>position of the AHJ next time round?  I still believe our initial
>installation represents the safest configuration.
>
>Carl Adams
>SunRock Solar, LLC
>_
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20100113/71790e4d/attachment.htm>


More information about the RE-Wrenches mailing list