[RE-wrenches] 2011 code and roof discos
Bill Brooks
billbrooks7 at yahoo.com
Wed Jan 13 21:38:19 EST 2010
Kirk,
Disconnects within sight of combiner boxes will be required in 2011. Another
good reason to keep combiner boxes off residential rooftops. This is
targeting commercial rooftops where large system have no disconnects for
servicing fuses.
Bill.
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Kirk
Herander, VSE
Sent: Wednesday, January 13, 2010 2:33 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] 2011 code and roof discos
On that note Bill, will roof disconnects be required in the 2011 NEC?
Kirk Herander
Vermont Solar Engineering
802.863.1202
NABCEP(tm) Certified Solar Installer
NYSERDA-eligible Installer
VT Solar Incentive Program Partner
_____
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Bill Brooks
Sent: Wednesday, January 13, 2010 12:36 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Solar accumulation panel
Andrew,
It does not exist. We tried like crazy to get it into the 2011 NEC, but to
no avail. At the last second the proposal was put on hold until the 2014
NEC. Major bummer. For now it can only be done with AHJ approval. Many allow
it but it is not in the NEC. Alternatively you must use the sum of supply
breakers no greater than 120%. Much more restrictive.
Bill.