[RE-wrenches] Power Factor and Grid Tied PV
Marco Mangelsdorf
marco at pvthawaii.com
Fri Jan 8 12:51:50 EST 2010
According to an article, written by a utility engineer on O'ahu, PF can be
worsened at the site where a substantial PV system is located.
If there is a poor or wavering PF due to an abundance of inductive loads at
a particular site, having a large inverter, in relation to the overall power
consumption of the facility, can actually make the PF worse.
I can track down that piece for anyone interested.
Marco
ProVision Solar
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Joel
Davidson
Sent: Thursday, January 07, 2010 5:42 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] Power Factor and Grid Tied PV
We worked on dozens of commercial PV systems in Southern California Edison
(SCE), Los Angeles Department of Water & Power (LADWP), and San Diego Gas &
Electric (SDG&E) territories. We installed Xantrex, SMA, and SatCon
inverters and measured power factor on both the grid and the inverters. In
every case, inverter power factor was 1. In almost every case LADWP's power
factor was less than 1 and in older parts of Los Angeles power factor was
often 0.75. SCE and SDG&E generally has pretty good power factors. In
general, PV inverters do not worsen grid power factor. In general, newer
sections of the grid are better designed and better managed than older grid
sections. When utility companies or anyone says PV causes grid problems, ask
for proof.
Joel Davidson
----- Original Message -----
From: "Darryl Thayer" <daryl_solar at yahoo.com>
To: "RE-wrenches" <re-wrenches at lists.re-wrenches.org>
Sent: Wednesday, January 06, 2010 9:39 PM
Subject: Re: [RE-wrenches] Power Factor and Grid Tied PV
I recently spoke with an inverter manufacture and I left with the following
opinion. Normally the inverter takes the unity power factor load and leaves
the reactive load. making the power factor worse. However the power factor
could be corrected by the inverter, However this would add cost to the
inverter and would not appear to have value to the solar industry. There
are variable reactance devices existing that can correct power factor, is
there need for another device?
Darryl
> Hello Wrenches,
>
> Commercial power customers often are penalized for low
> power factors.
> Looking for other info I came across this article, which
> seems to
> cover the subject from an academic standpoint.
> http://tinyurl.com/ye5pzrw Does anyone
> have real world data which
> might shed light on the impact of a DGT PV system on power
> factor.
>
> With Regards
> Carl Adams
> SunRock Solar, LLC.
> _______________________________________________
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches at lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
No virus found in this incoming message.
Checked by AVG - www.avg.com
Version: 9.0.725 / Virus Database: 270.14.129/2606 - Release Date: 01/07/10
21:35:00
More information about the RE-Wrenches