[RE-wrenches] dual stacked inverters on 208V service

David Katz dkatz at aeesolar.com
Thu Dec 31 18:01:07 EST 2009


Nik,
Since you cannot operate 2 inverters in a 3 phase mode, they will need 
to operate independently, so don't try to sync them.  Operate both 
independently.  if the building is set up for 120/208 there is not 240 
anyway.  You could stack them in 120V synchronized and connected across 
a single phase.  you may be able to stack them at 240 and only connect 
one of the inputs to AC in.
good luck.
David

David Katz

Chief Technical Officer

AEE Solar

1155 Redway Drive

P.O. Box 339

Redway, CA  95560

Tel (707) 825-1200

Fax (707) 825-1202

dkatz at aeesolar.com <mailto:david at aeesolar.com>

www.aeesolar.com <http://www.aeesolar.com/>

 

DISCLAIMER:
This communication, along with any documents, files or attachments, is 
intended for the use of only the addressee and contains privileged and 
confidential information. If you are not the intended recipient, you are 
hereby notified that any dissemination, distribution or copying of any 
information contained in or attached to this communication is strictly 
prohibited.  If you have received this message in error, please notify 
the sender immediately by e-mail reply and destroy the original 
communication and its attachments without reading, printing or saving in 
any manner.

 



Nik Ponzio wrote:
> Hi Gang,
>
> I have a problem. We are installing a gridtie PV system with 2 
> battery-based inverters for 240V. The service coming in to the condo 
> is 120/208 split-phase fed from 3-phase 208 in main building. The 
> master inverter pickups up L1 but the slave inverter will not sync. 
> What am I missing?
>
> Thanks and Happy New Year to all!
>
> ------------------------------------------------------------------------
>
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>   
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20091231/09a01a6c/attachment-0001.htm>


More information about the RE-Wrenches mailing list