[RE-wrenches] Strings and series of batteries
William Miller
william at millersolar.com
Thu Dec 3 11:41:47 EST 2009
Friends:
Regardless of what material you prefer to protect battery posts, I don't
recommend applying it until after the connection is torqued. The cable
ends and the terminals need to be wire brushed immediately prior to
assembly. We had to dis-assemble a set of batteries and move them for 48
hours. The terminals had been cleaned the previous day. After sitting
under a cover for 48 hours, when re-assembled, the terminals had enough
invisible corrosion to cause a significant inability to charge
correctly. After cleaning the terminals the problem was corrected. We use
a small Makita grinder with a wire brush. This does require care to avoid
arcing and brushing away knuckle skin.
Napa Auto has a spray-on terminal protectant that skins over nicely, making
less of a mess when checking electrolyte levels. It also has an attractive
cranberry color.
William Miller
At 01:21 AM 12/3/2009, you wrote:
>I was just picking up on where everybody is located. The cold weather boys
>like vaseline, and obviously you warm weather folks need the grease.
>I think this affects the battery sizing debate too: if I size a battery
>for 4 days storage, it only has 2 or 3 days of storage in really cold weather.
>
>R. Walters
>ray at solarray.com
>Solar Engineer