Two answers, Jay,

Actually both.

For a lot of systems, we use the ILSCO or POLARIS multi-barrel insulated
mechanical compression device that holds up to 8 or more cables up to
whatever size you purchase them in.

Then, for larger systems, we use standard, 1/4 x 4" copper bus bar with
isolating bushing, drilled out to match the crimp-on lugs of 2-hole
connectors.

Both are comparable quality, and all the parts are UL listed.

Walt

-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of jay peltz
Sent: Wednesday, December 02, 2009 6:24 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Strings and series of batteries

My question about the buss bar is this.

Is this something that you are fabricating or are buying and if so where and
what?