[RE-wrenches] Strings and series of batteries
James Surrette
james at surrette.com
Wed Dec 2 19:32:03 EST 2009
Hi Tump et al.
In the UK, so sorry for slow response.
Must echo your comments. A series string is, without a doubt, the most
efficient and things just get more complicated (connections, numbers of
cells, voltage disparity) as you add parallel strings. Per Tom's
comments, the only solution to multiple banks is bus bars
Regards,
Jamie
James Surrette
Surrette Battery Co. Ltd
1 Station Rd.
Springhill, NS, CAN
B0M 1X0
Direct: 902.597.4027
Fax: 902.597.8447
>>> "Tump" <tump at hughes.net> 12/2/2009 8:32 AM >>>
Surrette Battery, THE battery company suggests NO MORE the 3 parallel
in a string & would like to see 2 preferably.
If there are more the 3 then they really not interested in warrantee
issues.
Jamie where are you??????
Now a days there are plenty of options for a good size/AH BB that can
be configured in 1 or 2 parallel strings.
Its just that us old guys are having a harder time w/ gravity!
Tump at swnl.net www.SWNL.net ( http://www.swnl.net/ )
Solarwinds Northernlights
Serving Mid Coast Maine & Northern California
Me.# 207-832-7574 Cl.# 610-517-8401
Blair "TUMP" May
******** MAINE'S CHARTER ********
NABCEP "Certified PV Installer"
******** MAINE'S CHARTER ********
Trace Xantrex "Certified" Dealer / Installer"
-----Original Message-----
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Dana
Sent: Tuesday, December 01, 2009 12:58 PM
To: 'RE-wrenches'
Subject: [RE-wrenches] Strings and series of batteries
On a similar subject here â
Long ago, I had a Trojan battery rep. state that they did not like to
see more than [12] L-16s in a series âparallel bank system. This was due
to too many points of connection / resistance and bad communication
due to multiple flow paths.
Has anyone else heard similar or contrary information/recommendations?
Thanks
Dana Orzel
Great Solar Works, Inc
www.solarwork.com
E - dana at solarwork.com
V - 970.626.5253
F - 970.626.4140
C - 970.209.4076
I will be the shift in how the world uses power! - Dana Orzel
From: re-wrenches-bounces at lists.re-wrenches.org
[mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Larry
Crutcher, Starlight Solar
Sent: Tuesday, December 01, 2009 10:42 AM
To: RE-wrenches
Subject: Re: [RE-wrenches] concord batteries, EQUALIZE Them!
If the 180 watt panel will provide enough current to run the recovery
process, then give it a try. What I expect is that your current will
vary throughout the day. Not sure if this is a critical point or if it
will just prolong the process. Pay attention to the temperature. I use a
laser temp probe on the terminals every 30 minutes to verify.
Another thing to monitor is the current. It will probably start very
low and build over time due to high resistance from sulfated plates.
During this time the voltage might get really high and then lower some.
Don't worry about the voltage. After a while the current will begin to
drop. This means the recovery process is working.
I just realized that this battery bank must be 4 in series and ten
parallel strings. This is a horrible design that can never work right
without extensive monthly maintenance. The strings with higher
resistance will not be charged properly. Because of this, many strings
will be undercharged every day. EVERY day! So even if you recover these
batteries, someone will need to test and equalize at least every month.
I really want to stress this point as multiple parallel batteries are
the ruin and waste of many thousands of tons of batteries each year. I
never design for more than two strings in parallel. Do this and be
happy.
Larry Crutcher
www.starlightsolar.com
larry at starlightsolar.com
(928) 941-1660
<br><br>This email and its attachments have been scanned by iConnection E-Mail Firewall for viruses, spam, and malicious content.
<br><br>The information transmitted in this email is intended only for the entity or person to which it is addressed and may contain confidential/privileged material. If you received this in error, please contact the sender and delete the material from any computer. Any review, retransmission, dissemination, or other use of this information by persons or entities other than the intended recipient is strictly prohibited. %^^%
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches_lists.re-wrenches.org/attachments/20091202/9cab6735/attachment-0001.htm>
More information about the RE-Wrenches
mailing list